Can you always share a neutral with two single phase circuits?

Joined: Jul 2004
Posts: 787
L
Member
NO.

Joined: Jul 2005
Posts: 183
J
Member
to expand on the NO, some cases where you would not share a neutral are ground fault home run circuits, arc fault home run circuits, and if your two circuits were both L1 or both L2.