ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
250.104
by gfretwell. 02/16/19 01:08 PM
PurpleAir Recalls Power Supply Units
by Admin. 02/14/19 08:43 PM
Utility Company Programs
by katty81. 02/14/19 11:11 AM
AFDD's coming to the UK
by Trumpy. 02/14/19 12:29 AM
Delta Electronics Recalls Solar Inverters
by electech. 02/13/19 10:26 AM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 6 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
revist iso transformer #165285
06/25/07 01:05 AM
06/25/07 01:05 AM
watersparkfalls  Offline OP
Member
Joined: Mar 2005
Posts: 222
Washington...Not DC
my iso transformer passed inspection with everything bonded(frame,equipment bonding from panel,x2,x3,bonding bushing,neut to sub and equipmet bonding to sub)all done at the transformer.
but according to acme (depending on tech that answers phone) i should drive ground rod and have new ground reference for true isolation.
so here is my question this time around.
what if i drive a new ground rod(as tech specified) and from this new ground rod, i run a wire to the other ground rod already driven(which is bonded with cold water via main panel)now i seperate egc's at transformer and intentally ground x2,x3 to new ground rod for isolated neut at sub panel? the house would still have a single grounded reference point and it should be electrically safe and nec complient wouldn't it? i am doing everything to install so i do have an isolated system...thus any noise that could/should appear later on will not be because of installation. KEEPING in mind Safety is my first priority!
what is your guys opinion of this idea?

2017 / 2014 NEC & Related Books and Study Guides
Re: revist iso transformer [Re: watersparkfalls] #165300
06/25/07 10:13 AM
06/25/07 10:13 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
First the transformer secondary requires a connection to a grounding electrode. Second both the primary and secondary EGCs must be connected to the transformer frame and case. In fact a truely isolated system is not possible if you are in compliance with the NEC with some very rare exceptions such as hospital operating rooms.
Don


Don(resqcapt19)

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
andey 3
Popular Topics(Views)
253,217 Are you busy
189,873 Re: Forum
179,572 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.017s Queries: 15 (0.003s) Memory: 0.9433 MB (Peak: 1.0603 MB) Zlib enabled. Server Time: 2019-02-17 09:47:02 UTC