ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
dsk 13
Admin 4
Recent Posts
electircal ageing test on IPC
by SIAME. 08/15/17 02:43 AM
electrical aging test on IPC
by gfretwell. 08/15/17 12:27 AM
Bathroom electrical
by gfretwell. 08/14/17 02:05 AM
"Line level" audio on Cat 5?
by gfretwell. 08/08/17 10:39 PM
Fire alarm phone lines and color coding
by gfretwell. 08/08/17 10:26 PM
New in the Gallery:
Housebilding DIY wiring
Popular Topics(Views)
239,859 Are you busy
175,419 Re: Forum
167,707 Need opinion
Who's Online Now
0 registered members (), 39 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#165285 - 06/25/07 02:05 AM revist iso transformer  
watersparkfalls  Offline
Member
Joined: Mar 2005
Posts: 216
Washington...Not DC
my iso transformer passed inspection with everything bonded(frame,equipment bonding from panel,x2,x3,bonding bushing,neut to sub and equipmet bonding to sub)all done at the transformer.
but according to acme (depending on tech that answers phone) i should drive ground rod and have new ground reference for true isolation.
so here is my question this time around.
what if i drive a new ground rod(as tech specified) and from this new ground rod, i run a wire to the other ground rod already driven(which is bonded with cold water via main panel)now i seperate egc's at transformer and intentally ground x2,x3 to new ground rod for isolated neut at sub panel? the house would still have a single grounded reference point and it should be electrically safe and nec complient wouldn't it? i am doing everything to install so i do have an isolated system...thus any noise that could/should appear later on will not be because of installation. KEEPING in mind Safety is my first priority!
what is your guys opinion of this idea?


2017 / 2014 NEC & Related Books and Study Guides

#165300 - 06/25/07 11:13 AM Re: revist iso transformer [Re: watersparkfalls]  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
First the transformer secondary requires a connection to a grounding electrode. Second both the primary and secondary EGCs must be connected to the transformer frame and case. In fact a truely isolated system is not possible if you are in compliance with the NEC with some very rare exceptions such as hospital operating rooms.
Don


Don(resqcapt19)


Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.009s Queries: 15 (0.002s) Memory: 0.7448 MB (Peak: 0.8603 MB) Zlib enabled. Server Time: 2017-08-16 23:48:32 UTC