#165285 06/25/07 01:05 AM
Joined: Mar 2005
Posts: 240
Member
my iso transformer passed inspection with everything bonded(frame,equipment bonding from panel,x2,x3,bonding bushing,neut to sub and equipmet bonding to sub)all done at the transformer.
but according to acme (depending on tech that answers phone) i should drive ground rod and have new ground reference for true isolation.
so here is my question this time around.
what if i drive a new ground rod(as tech specified) and from this new ground rod, i run a wire to the other ground rod already driven(which is bonded with cold water via main panel)now i seperate egc's at transformer and intentally ground x2,x3 to new ground rod for isolated neut at sub panel? the house would still have a single grounded reference point and it should be electrically safe and nec complient wouldn't it? i am doing everything to install so i do have an isolated system...thus any noise that could/should appear later on will not be because of installation. KEEPING in mind Safety is my first priority!
what is your guys opinion of this idea?

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Nov 2000
Posts: 2,148
R
Member
First the transformer secondary requires a connection to a grounding electrode. Second both the primary and secondary EGCs must be connected to the transformer frame and case. In fact a truely isolated system is not possible if you are in compliance with the NEC with some very rare exceptions such as hospital operating rooms.
Don


Don(resqcapt19)

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RonKipperDatacom
RonKipperDatacom
Kansas City, KS
Posts: 30
Joined: January 2013
Top Posters(30 Days)
Trumpy 6
NORCAL 3
Popular Topics(Views)
300,650 Are you busy
230,348 Re: Forum
215,105 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5