#164980 - 06/15/07 08:08 PM Sizing of service lateral from 320 Amp meter base?  
homer  Offline
Member
Joined: Sep 2004
Posts: 68
Vancouver, WA, USA
Can anybody tell me how to size the service cable from the feed through meter to two 200-amp panels at a residence. I am removing the existing CT's and meter because an addition will put the meter inside of the house. They are also going to a heat pump and removing the circuits for the electric ceiling heat for a house that is about 3000 square feet. So the load will be reduced at least 50%. The service calculates at about 140 amps max. I am planning on leaving both of the existing 200-amp panels which will be fed from this service lateral. Thanks for your help guys!


2017 / 2014 NEC & Related Books and Study Guides

#165137 - 06/19/07 06:16 PM Re: Sizing of service lateral from 320 Amp meter base? [Re: homer]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,857
Brick, NJ USA
Common install here (NJ) is 200 amp SEU cable (4/0 al-2 insulated, 1 bare) to each 200 amp MCB panel. Provided that panels are within acceptable distance. Option would be conduit & 4/0 al conductors.

I'm assuming that you are talking about the 'load' side of the meter, and the disconnects are in each panel?

John


John

#165150 - 06/20/07 04:28 PM Re: Sizing of service lateral from 320 Amp meter b [Re: HotLine1]  
EV607797  Offline
Member
Joined: Oct 2006
Posts: 745
Fredericksburg, VA, USA
4/0 SEU (AL) or 2/0 SEU (CU) to each panel is the norm here in Virginia as well. We are lucky, the power company handles all final connections at the meter, so all we have to do is mount the meter socket and bring the cables into it. They do the rest.


---Ed---

"But the guy at Home Depot said it would work."

#165187 - 06/22/07 02:30 AM Re: Sizing of service lateral from 320 Amp meter b [Re: EV607797]  
homer  Offline
Member
Joined: Sep 2004
Posts: 68
Vancouver, WA, USA
Thanks for your input, guys. I have a single 3" conduit, so I did some research in section 230 on service ampacity. As long as the computed load is less than the service ampacity, the cable can have a smaller ampacity than the overcurrent rating of the service. I didn't want to run parallel cables from the 320-amp meter to each panel. It looks like 350-alum will be plenty big for the two panels. It will splice in the old CT cabinet. (The CT's are going away). Thanks again for your replies!



Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 15 (0.003s) Memory: 0.7620 MB (Peak: 0.8939 MB) Zlib enabled. Server Time: 2017-08-16 23:50:32 UTC