PVC for service entrance #164696 06/08/07 10:01 PM
Joined: Sep 2005
Posts: 202
W
WFO Offline OP
Member
Our POCO requires metallic conduit for a service entrance to the meter. It does not allow a two way feed (as you would have on a overhead meter pole) in the same conduit, so many customers have the service coming into the meter in metallic tubing and the exiting wire going back up the pole in a seperate PVC conduit. We are having an argument on if PVC conduit is permissible for this purpose. If there is applicable code, please list the sections. Thanks.

Work Gear for Electricians and the Trades
Re: PVC for service entrance [Re: WFO] #164700 06/08/07 10:41 PM
Joined: Jul 2004
Posts: 9,392
G
gfretwell Offline
Member
Sch 80?
This will come down to the old "physical damage" judgement call.


Greg Fretwell
Re: PVC for service entrance [Re: gfretwell] #164713 06/09/07 07:51 AM
Joined: Sep 2005
Posts: 202
W
WFO Offline OP
Member
I don't think the size was discussed but I'm assuming everyone was thinking Schedule 80. Does the "judgement" remark mean it is not specifically prohibited, but left to the discretion of the installer?

Re: PVC for service entrance [Re: WFO] #164718 06/09/07 01:44 PM
Joined: Jul 2004
Posts: 9,392
G
gfretwell Offline
Member
The installer in conjunction with the AHJ policy.
"Subject to physical damage" and what makes that "severe physical damage" is like pornography.
Nobody can define it but every AHJ thinks he knows it when he sees it. Few can actually agree what it is.


Greg Fretwell
Re: PVC for service entrance [Re: gfretwell] #164720 06/09/07 02:58 PM
Joined: Jan 2002
Posts: 1,457
E
Electricmanscott Offline
Member
I ususally use sch 40 PVC for all my services. Unless there is a walkway or driveway in that side of the building then sch 80 it is.

Re: PVC for service entrance [Re: Electricmanscott] #164791 06/11/07 02:54 PM
Joined: Oct 2002
Posts: 482
Z
Zapped Offline
Member
Out here in Cali, the AHJ usually backs up the requirements set forth by the POCO. Period. Here, it's sch. 80 for anything that is exposed, and sch. 40 for the underground. The POCO lays out the specifics for the diameter of the pipe (min. 2", most apps are 3") radius of the sweeps, allowable total deflection of the bends (180 deg for SDGE, unless approved for an extra 45 or two), placement and manufaturer/model of the hand holes, and pretty much everything else. They even do their own independent trench inspections, on top of the AHJs.

So, to give you an answer you may not like, if the POCO says it's so, then it is usually so, and no amount of debate is likely to put a dent in that.

Results may vary by location...

Re: PVC for service entrance [Re: Zapped] #164806 06/11/07 08:17 PM
Joined: Jul 2004
Posts: 9,392
G
gfretwell Offline
Member
I was just doing a little research for my golf bathroom service deal and it turns out FPL provides your conduit as part of the service charge. You pay them the labor charge to do the work.
Then you can do the work yourself, If that meets their satisfaction they refund your labor money, minus what it cost them to bring your job up to their standard.
I found that whole process strange.

http://www.fpl.com/doingbusiness/builder/b1_index.shtml


Greg Fretwell
Re: PVC for service entrance [Re: gfretwell] #164816 06/11/07 10:00 PM
Joined: Feb 2003
Posts: 288
Y
yaktx Offline
Member
See, this is why it pays to read before you type. I was about to write that if Schedule 40 is acceptable for service conductors under the NEC, it should be OK for a feeder even if your local POCO regs call for metallic conduit. Then I looked and the 2002 NEC says Schedule 80. Turns out that is a change in the 2002 Code.

I didn't know, because the last time I worked anyplace that allowed PVC for a service riser was in 1997. Then again, I've never been red-tagged for a Schedule 40 lateral rising above-grade, which to my knowledge remains entirely legal in my neck of the woods.

Re: PVC for service entrance [Re: yaktx] #164875 06/13/07 12:04 PM
Joined: Jun 2006
Posts: 613
M
mikesh Offline
Member
PVC is used often here in BC but we never see schedule 80 except in water piping. Mech protection may be required.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
Popular Topics(Views)
258,695 Are you busy
194,264 Re: Forum
183,725 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3