PVC for service entrance #164696
06/08/07 10:01 PM
06/08/07 10:01 PM
W
WFO  Offline OP
Member
Joined: Sep 2005
Posts: 202
Cat Spring, TX
Our POCO requires metallic conduit for a service entrance to the meter. It does not allow a two way feed (as you would have on a overhead meter pole) in the same conduit, so many customers have the service coming into the meter in metallic tubing and the exiting wire going back up the pole in a seperate PVC conduit. We are having an argument on if PVC conduit is permissible for this purpose. If there is applicable code, please list the sections. Thanks.

Work Gear for Electricians and the Trades
Re: PVC for service entrance [Re: WFO] #164700
06/08/07 10:41 PM
06/08/07 10:41 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,289
Estero,Fl,usa
Sch 80?
This will come down to the old "physical damage" judgement call.


Greg Fretwell
Re: PVC for service entrance [Re: gfretwell] #164713
06/09/07 07:51 AM
06/09/07 07:51 AM
W
WFO  Offline OP
Member
Joined: Sep 2005
Posts: 202
Cat Spring, TX
I don't think the size was discussed but I'm assuming everyone was thinking Schedule 80. Does the "judgement" remark mean it is not specifically prohibited, but left to the discretion of the installer?

Re: PVC for service entrance [Re: WFO] #164718
06/09/07 01:44 PM
06/09/07 01:44 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,289
Estero,Fl,usa
The installer in conjunction with the AHJ policy.
"Subject to physical damage" and what makes that "severe physical damage" is like pornography.
Nobody can define it but every AHJ thinks he knows it when he sees it. Few can actually agree what it is.


Greg Fretwell
Re: PVC for service entrance [Re: gfretwell] #164720
06/09/07 02:58 PM
06/09/07 02:58 PM
E
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
I ususally use sch 40 PVC for all my services. Unless there is a walkway or driveway in that side of the building then sch 80 it is.

Re: PVC for service entrance [Re: Electricmanscott] #164791
06/11/07 02:54 PM
06/11/07 02:54 PM
Z
Zapped  Offline
Member
Joined: Oct 2002
Posts: 482
Huntington Beach, CA, USA
Out here in Cali, the AHJ usually backs up the requirements set forth by the POCO. Period. Here, it's sch. 80 for anything that is exposed, and sch. 40 for the underground. The POCO lays out the specifics for the diameter of the pipe (min. 2", most apps are 3") radius of the sweeps, allowable total deflection of the bends (180 deg for SDGE, unless approved for an extra 45 or two), placement and manufaturer/model of the hand holes, and pretty much everything else. They even do their own independent trench inspections, on top of the AHJs.

So, to give you an answer you may not like, if the POCO says it's so, then it is usually so, and no amount of debate is likely to put a dent in that.

Results may vary by location...

Re: PVC for service entrance [Re: Zapped] #164806
06/11/07 08:17 PM
06/11/07 08:17 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,289
Estero,Fl,usa
I was just doing a little research for my golf bathroom service deal and it turns out FPL provides your conduit as part of the service charge. You pay them the labor charge to do the work.
Then you can do the work yourself, If that meets their satisfaction they refund your labor money, minus what it cost them to bring your job up to their standard.
I found that whole process strange.

http://www.fpl.com/doingbusiness/builder/b1_index.shtml


Greg Fretwell
Re: PVC for service entrance [Re: gfretwell] #164816
06/11/07 10:00 PM
06/11/07 10:00 PM
Y
yaktx  Offline
Member
Joined: Feb 2003
Posts: 288
Austin, Texas, USA
See, this is why it pays to read before you type. I was about to write that if Schedule 40 is acceptable for service conductors under the NEC, it should be OK for a feeder even if your local POCO regs call for metallic conduit. Then I looked and the 2002 NEC says Schedule 80. Turns out that is a change in the 2002 Code.

I didn't know, because the last time I worked anyplace that allowed PVC for a service riser was in 1997. Then again, I've never been red-tagged for a Schedule 40 lateral rising above-grade, which to my knowledge remains entirely legal in my neck of the woods.

Re: PVC for service entrance [Re: yaktx] #164875
06/13/07 12:04 PM
06/13/07 12:04 PM
M
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
PVC is used often here in BC but we never see schedule 80 except in water piping. Mech protection may be required.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,247
Joined: July 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
Trumpy 11
Popular Topics(Views)
249,392 Are you busy
187,329 Re: Forum
176,666 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 15 (0.004s) Memory: 1.0033 MB (Peak: 1.1757 MB) Zlib enabled. Server Time: 2018-09-23 12:36:54 UTC