Loomex Bundling #164588
06/06/07 07:07 PM
06/06/07 07:07 PM
dougwells  Offline
OP
Member
Joined: May 2003
Posts: 1,142
kamloops BC Canada
I may have a job cleaning up work after a homeowners permit was canceled by the safety authority.
this is what i saw in the Basement.
1 8/3... 1 14/3....2 14/2 in a one inch hole.There is also minor jacket damage.

another hole theres 1 8/3 1 14/3 and 1 14/2 in a one inch hole.
the reason i ask is i would never do this as i use many holes anyhow will this be a code correction. Thanks

Tools for Electricians:
Re: Loomex Bundling [Re: dougwells] #164597
06/06/07 08:58 PM
06/06/07 08:58 PM
J
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
4-004(10) permits bundling but not beyond 60mm without derating. There is the obvious repair with the damaged cable sheath, but if you can run it through the hole without damage to the cable, it is acceptable, if not always abvisable.

Re: Loomex Bundling [Re: jay8] #164598
06/06/07 08:59 PM
06/06/07 08:59 PM
J
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
whoops, thats 600 mm without derating, not 60 mm.

Re: Loomex Bundling [Re: jay8] #164623
06/07/07 11:56 AM
06/07/07 11:56 AM
M
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
In order to get the 80% on the wires I generally say 2X3 wire or 3X2 wire run together. No 100% rated breakers or 3 current carrying conductors max run together.
The hole should be big enough to allow all the conductors to run freely. I stop short of asking for max 40% fill of the hole diameter but it is still a good ideal to allow for holes big enough to easily allow the addition of another cable or two.
No derating on communications cables but they can stuff too many cables in a hole too.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 15
Potseal 15
Popular Topics(Views)
243,601 Are you busy
180,416 Re: Forum
170,871 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 15 (0.004s) Memory: 0.9587 MB (Peak: 1.0925 MB) Zlib enabled. Server Time: 2018-01-23 20:00:16 UTC