ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Is this safe?
by gfretwell. 04/26/18 02:04 AM
Inspections and Testing
by HotLine1. 04/25/18 08:41 AM
FEMA height and electrical equiment.,
by HotLine1. 04/20/18 08:49 AM
This anti-theist is priceless!!!
by LongRunner. 04/19/18 04:02 PM
Recall notice: Square D Services Switches
by gfretwell. 04/18/18 01:24 PM
New in the Gallery:
Housebilding DIY wiring
SE cable question
Who's Online Now
0 registered members (), 10 guests, and 12 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Loomex Bundling #164588
06/06/07 08:07 PM
06/06/07 08:07 PM
dougwells  Offline
OP
Member
Joined: May 2003
Posts: 1,143
kamloops BC Canada
I may have a job cleaning up work after a homeowners permit was canceled by the safety authority.
this is what i saw in the Basement.
1 8/3... 1 14/3....2 14/2 in a one inch hole.There is also minor jacket damage.

another hole theres 1 8/3 1 14/3 and 1 14/2 in a one inch hole.
the reason i ask is i would never do this as i use many holes anyhow will this be a code correction. Thanks

Tools for Electricians:
Re: Loomex Bundling [Re: dougwells] #164597
06/06/07 09:58 PM
06/06/07 09:58 PM
J
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
4-004(10) permits bundling but not beyond 60mm without derating. There is the obvious repair with the damaged cable sheath, but if you can run it through the hole without damage to the cable, it is acceptable, if not always abvisable.

Re: Loomex Bundling [Re: jay8] #164598
06/06/07 09:59 PM
06/06/07 09:59 PM
J
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
whoops, thats 600 mm without derating, not 60 mm.

Re: Loomex Bundling [Re: jay8] #164623
06/07/07 12:56 PM
06/07/07 12:56 PM
M
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
In order to get the 80% on the wires I generally say 2X3 wire or 3X2 wire run together. No 100% rated breakers or 3 current carrying conductors max run together.
The hole should be big enough to allow all the conductors to run freely. I stop short of asking for max 40% fill of the hole diameter but it is still a good ideal to allow for holes big enough to easily allow the addition of another cable or two.
No derating on communications cables but they can stuff too many cables in a hole too.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
245,936 Are you busy
183,030 Re: Forum
172,784 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 15 (0.004s) Memory: 0.9586 MB (Peak: 1.0921 MB) Zlib enabled. Server Time: 2018-04-26 13:16:53 UTC