#164588 - 06/06/07 08:07 PM Loomex Bundling  
dougwells  Offline


Member
Joined: May 2003
Posts: 1,140
kamloops BC Canada
I may have a job cleaning up work after a homeowners permit was canceled by the safety authority.
this is what i saw in the Basement.
1 8/3... 1 14/3....2 14/2 in a one inch hole.There is also minor jacket damage.

another hole theres 1 8/3 1 14/3 and 1 14/2 in a one inch hole.
the reason i ask is i would never do this as i use many holes anyhow will this be a code correction. Thanks


Tools for Electricians:

#164597 - 06/06/07 09:58 PM Re: Loomex Bundling [Re: dougwells]  
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
4-004(10) permits bundling but not beyond 60mm without derating. There is the obvious repair with the damaged cable sheath, but if you can run it through the hole without damage to the cable, it is acceptable, if not always abvisable.


#164598 - 06/06/07 09:59 PM Re: Loomex Bundling [Re: jay8]  
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
whoops, thats 600 mm without derating, not 60 mm.


#164623 - 06/07/07 12:56 PM Re: Loomex Bundling [Re: jay8]  
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
In order to get the 80% on the wires I generally say 2X3 wire or 3X2 wire run together. No 100% rated breakers or 3 current carrying conductors max run together.
The hole should be big enough to allow all the conductors to run freely. I stop short of asking for max 40% fill of the hole diameter but it is still a good ideal to allow for holes big enough to easily allow the addition of another cable or two.
No derating on communications cables but they can stuff too many cables in a hole too.



Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 15 (0.003s) Memory: 0.7604 MB (Peak: 0.8950 MB) Zlib enabled. Server Time: 2017-10-23 18:58:02 UTC