Loomex Bundling #164588 06/06/07 07:07 PM
Joined: May 2003
Posts: 1,155
dougwells Offline OP
Member
I may have a job cleaning up work after a homeowners permit was canceled by the safety authority.
this is what i saw in the Basement.
1 8/3... 1 14/3....2 14/2 in a one inch hole.There is also minor jacket damage.

another hole theres 1 8/3 1 14/3 and 1 14/2 in a one inch hole.
the reason i ask is i would never do this as i use many holes anyhow will this be a code correction. Thanks

Tools for Electricians:
Re: Loomex Bundling [Re: dougwells] #164597 06/06/07 08:58 PM
Joined: Jul 2005
Posts: 183
J
jay8 Offline
Member
4-004(10) permits bundling but not beyond 60mm without derating. There is the obvious repair with the damaged cable sheath, but if you can run it through the hole without damage to the cable, it is acceptable, if not always abvisable.

Re: Loomex Bundling [Re: jay8] #164598 06/06/07 08:59 PM
Joined: Jul 2005
Posts: 183
J
jay8 Offline
Member
whoops, thats 600 mm without derating, not 60 mm.

Re: Loomex Bundling [Re: jay8] #164623 06/07/07 11:56 AM
Joined: Jun 2006
Posts: 613
M
mikesh Offline
Member
In order to get the 80% on the wires I generally say 2X3 wire or 3X2 wire run together. No 100% rated breakers or 3 current carrying conductors max run together.
The hole should be big enough to allow all the conductors to run freely. I stop short of asking for max 40% fill of the hole diameter but it is still a good ideal to allow for holes big enough to easily allow the addition of another cable or two.
No derating on communications cables but they can stuff too many cables in a hole too.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,352 Are you busy
209,224 Re: Forum
196,526 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3