Conduit Body Splice #164511
06/04/07 10:44 PM
06/04/07 10:44 PM
C
Cinner  Offline OP
Member
Joined: Dec 2004
Posts: 78
Kelowna, B.C., Canada
Can a splice be made in a conduit body for example an LB?

Tools for Electricians:
Re: Conduit Body Splice [Re: Cinner] #164517
06/05/07 01:52 AM
06/05/07 01:52 AM
dougwells  Offline

Member
Joined: May 2003
Posts: 1,149
kamloops BC Canada
No. But I cant reference a code section They cannot be used for a junction box.

Re: Conduit Body Splice [Re: dougwells] #164526
06/05/07 08:44 AM
06/05/07 08:44 AM
G
ghost307  Offline
Member
Joined: May 2005
Posts: 958
Chicago Illinois USA
314.5

There's a VERY limited exception in 314.16C2 that allows it.


Ghost307
Re: Conduit Body Splice [Re: ghost307] #164532
06/05/07 11:32 AM
06/05/07 11:32 AM
dougwells  Offline

Member
Joined: May 2003
Posts: 1,149
kamloops BC Canada
Now we need a Canadian Code reference

Re: Conduit Body Splice [Re: dougwells] #164533
06/05/07 11:59 AM
06/05/07 11:59 AM
M
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
Some conduit bodies are approved for splices. space and wire count is very limited. The body has to have a cubic inch capacity marked on it. There are no specific rules in the CEC that say no but there are none that say yes either. The trick here is, some bodies are approved for splices and many inspectors will respect the Approved use with some evidence suplied from the wholsale and installer.

Re: Conduit Body Splice [Re: mikesh] #164534
06/05/07 07:47 PM
06/05/07 07:47 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Take note that 314.16(C)(2) not only allows splices in condulets that are marked, it also allows devices to be installed in them.

[Linked Image]

Roger

Re: Conduit Body Splice [Re: Cinner] #164535
06/05/07 08:11 PM
06/05/07 08:11 PM
C
CRM  Offline
Member
Joined: Feb 2004
Posts: 74
Alberta Canada
According the Alberta Standata Code you can't. The code does not permit "conduit fittings" to be used as a junction box. However, in Alberta we have interpreted the term "equivalent device" in rule 12-3000(1) to include "conduit fittings" in special applications (i.e. connection to solenoids, photocells, etc) Wire leads from these devices must be integral to the device. Where the device has a bonding conductor and the conduit fitting has no provisions for attaching a bonding conductor, a separate bonding conductor must be provided in the conduit system to the fitting. The fitting must also comply with the requirements of rule 12-3034 and table 22.

Re: Conduit Body Splice [Re: Cinner] #164542
06/05/07 10:00 PM
06/05/07 10:00 PM
J
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
I would look at 12-910, and if the fitting is part of the raceway where conductors continue through then I would say no splices because the fitting is part of the raceway. But if the conduit stops at the LB, then you may have a case for splicing with sufficient space as per Mikesh's post.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,431
Joined: February 2004
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,498 Are you busy
188,055 Re: Forum
177,697 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 15 (0.003s) Memory: 0.9934 MB (Peak: 1.1591 MB) Zlib enabled. Server Time: 2018-10-20 13:38:17 UTC