Air conditioner condenser #164362
06/01/07 09:13 AM
06/01/07 09:13 AM
F
Frank Cinker  Offline OP
Member
Joined: Jul 2001
Posts: 311
Pennsylvania
We have a roof top air conditioner condenser 230 volts, 1ph, 28.9 RLA. When the unit starts a buzzing sound is heard in the conduit. There is no short circuit and the unit seems to run fine. What would cause the buzzing noise.

Work Gear for Electricians and the Trades
Re: Air conditioner condenser [Re: Frank Cinker] #164364
06/01/07 10:20 AM
06/01/07 10:20 AM
M
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
Current inrush sets up magnetic fields in the wires and you hear the wires moving in the raceways.

Re: Air conditioner condenser [Re: mikesh] #164398
06/02/07 02:38 PM
06/02/07 02:38 PM
F
Frank Cinker  Offline OP
Member
Joined: Jul 2001
Posts: 311
Pennsylvania
Would installing larger size conductors eliminate or reduce this effect?

Re: Air conditioner condenser [Re: Frank Cinker] #164402
06/02/07 03:14 PM
06/02/07 03:14 PM
mxslick  Offline
Member
Joined: Oct 2004
Posts: 803
Atomic City, ID USA
Frank:

No, but twisting or triplexing the conductors may help.

Check out THIS THREAD for some more info on the topic.

Re: Air conditioner condenser [Re: mxslick] #164409
06/02/07 04:32 PM
06/02/07 04:32 PM
C
CTwireman  Offline
Member
Joined: Feb 2002
Posts: 840
Connecticut, USA
I have witnessed the same thing in two different situations. One was in a hotel electric room. The conduit feeding the elevator would literally make a "clink- clink" sound every time it operated. I amprobed the conductors and the amperage was going from 0 to almost 100 amps.

The other time was for a large pneumatic control system air compressor. The conduit was making more of a buzzing sound every time the compressor started.

My question is: Is this bad for the conductor insulation as the conductor moves around in the conduit?


Peter
Re: Air conditioner condenser [Re: CTwireman] #164439
06/03/07 02:48 PM
06/03/07 02:48 PM
mxslick  Offline
Member
Joined: Oct 2004
Posts: 803
Atomic City, ID USA
Peter:

Good question...my guess would be that IF there are no burrs, rough spots or separated sections at couplings, it probably would not make a huge difference in insulation wear. Couductors will expand/contract slightly during normal use so.....

But then again, has anyone encountered any failures caused by the conductors shorting out or to the conduit, where it's possible that this rattling was the primary cause?

Iwire, togol, any such experience in your areas?

Re: Air conditioner condenser [Re: mxslick] #164447
06/03/07 05:45 PM
06/03/07 05:45 PM
togol  Offline
Member
Joined: Sep 2005
Posts: 421
NW In. USA
hear it all the time, maybe more with 1ph loads than 3 ph, but since conductors do vibrate with a load on them anyway, I don't concern myself with it unless the rattling is excessive
I do know that some of them have been in service for more the ten years with no problems.and I would suggest that any vibration problems show up at the terminations and not inside a pipe, unless somebody forgot to ream the ends , as you wrote

I have also seen raceways that had disintegrated long ago with the exposed wires still looped through a coupling, outside, in the weather just humming along



Tom
Re: Air conditioner condenser [Re: Frank Cinker] #164493
06/04/07 05:55 PM
06/04/07 05:55 PM
J
joncon  Offline
Junior Member
Joined: Feb 2007
Posts: 20
Phoenix, AZ
Quote
Would installing larger size conductors eliminate or reduce this effect?


I say YES.


Disclaimer:

What the hell do I know.

Re: Air conditioner condenser [Re: joncon] #164540
06/05/07 08:46 PM
06/05/07 08:46 PM
W
wendel  Offline
Member
Joined: Aug 2004
Posts: 55
You might try a hard start kit for the compressor motor. Could save a lot of time and expense.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 9
Popular Topics(Views)
244,092 Are you busy
181,135 Re: Forum
171,327 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.024s Queries: 15 (0.003s) Memory: 1.0019 MB (Peak: 1.1732 MB) Zlib enabled. Server Time: 2018-02-25 23:39:31 UTC