#164263 05/29/07 03:16 PM
Joined: Jul 2002
Posts: 241
S
SJT Offline OP
Member
Hello and hope everyone is doing good. I am working on an estimate, where the customer wants to install a single Diesel pump, along with an above ground 1000 gallon tank. They will have a slab poured for this, and a 1/0 bare copper put into the slab, with a tail to bond the tank, and an eight foot ground rod, attached to the ring. This will create the grounding electrode for the slab. I do not bond the pump to that, do I? I was not sure, since this will all be set up for a hazardous location. Class 1 Div 2. Thanks for any input.

SJT #164355 06/01/07 06:46 AM
Joined: Jul 2002
Posts: 680
W
Member
Is the supplemental bonding some PEI or API code??