H
Member
I have a customer that wants an exhaust fan mounted directly above the shower stall. I can't find any codes that forbid this. This is a remodel in a small bath and there really isn't anywhere else to go with it.
Any thoughts welcome here.

2017 / 2014 NEC & Related Books and Study Guides
Joined: Jan 2004
Posts: 1,507
G
Member
There are several exhaust fans that are listed for use in shower stalls. The ones I've seen have a label inside the rough housing that will says-"Suitable for use in a shower or over a tub when installed on a GFCI protected circuit" or words to that effect. I know that Broan and Nutone make one for sure.


George Little
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
The code in question would be 110.3(B)

You would need to use a product listed for this location.

The following is excerpted from UL's White Book section on Fans, Electric (GPWV)

"Ceiling-insert fans, wall-insert fans, and ceiling-insert fan/light combinations intended to be mounted over bathtubs, showers, or within the zone above the bathtub and shower area as defined by Article 410 of the NEC, are marked "Acceptable for use over a bathtub or shower when installed in a GFCI protected branch circuit." These products are investigated to determine the effects of moisture (dampness or wetting), such as shower spray."

You can find the entire text of (GPWV) at
http://database.ul.com/cgi-bin/XYV/template/LISEXT/1FRAME/showpage.html?&name=GPWV.GuideInfo&ccnshorttitle=Fans,+Electric&objid=1074009331&cfgid=1073741824&version=versionless&parent_id=1073987360&sequence=1


Few things are harder to put up with than the annoyance of a good example.
Joined: Dec 2004
Posts: 209
H
Member
We use a lot of Panasonic fans over the shower and tub on a GFCI protected circuit. The smaller fans are rated at 0.3 sones. Extremely quiet.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,287
Joined: December 2000
Top Posters(30 Days)
timmp 3
Popular Topics(Views)
282,928 Are you busy
216,696 Re: Forum
203,120 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5