ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Square D "All-In-One" Panelboard
by NORCAL - 11/30/21 12:48 PM
Where is Everyone?
by luckyshadow - 11/21/21 10:14 AM
It's been an interesting career
by The Watt Doctor - 11/19/21 09:56 AM
Well I am back to stay (nearly 6 years)
by The Watt Doctor - 11/19/21 09:17 AM
Motor Load Relationships Between Fans and Pumps
by The Watt Doctor - 11/18/21 09:24 AM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
0 members (), 20 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#163784 05/16/07 08:21 PM
Joined: Oct 2000
Posts: 3,669
Likes: 2
Admin Offline OP
Administrator
Member
Quote
We often get calls to check switchboards that have had arcing faults and have insulators covered in carbon. Quite often electricians will tell us that they checked the bus with their ohm meter and all was clear. We try to tell them not to re-energize the board till the switchboard has been properly meggered either by us or I will supply a number for a firm that can perform the test (other than us) as sometimes electrical contractors think this HOO DOO VOO DOO we do is all about trying to separate them from their money and in these cases while money is an issue, my concern is their safety.

The test shown below was completed at 1000 VDC utilizing a megger, the carbon is pencil lead. The paper is a good insulator (meggered in the Gigaohms range) till it was contaminated with the pencil lead. The same test completed with an ohm meter showed no problems reading were acceptable. The difference is a 9 VDC ohm meter VS a 1000VDC megger.

- - BGaquin (Brian)

[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]

Admin #163787 05/17/07 02:55 AM
Joined: Sep 2005
Posts: 97
J
Member
Thats quite an impressive demonstration. I think I will sort out the cleaning of our switchgear now! it is full of grinding dust and smoke. I guess that under the right conditions, it could explode!


I took my time, I hurried up, The choice was mine, I didn't think enough
johno12345 #163789 05/17/07 06:44 AM
Joined: Dec 2005
Posts: 866
Likes: 4
R
Member
Very interesting test you have done there Brian.

Exactly what you show there is what happens in the real world.

I deal a lot with intermittend HT faults on 11 kV transformers. Dirty bushings cause a flasover, blow HT fuse. I always insist that the line crews disconnect the 11 kV cables prior to do an insulation test on the cable because of that reason.

I will do a similar test with a 5 kV megger, to show some of our fault staff why cables and bushings have to be clean.

Thanks for those great photo's

Regards, Raymond


The product of rotation, excitation and flux produces electricty.

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Top Posters(30 Days)
Admin 3
dsk 2
Popular Topics(Views)
286,325 Are you busy
218,789 Re: Forum
204,945 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5