Carbon Test #163784
05/16/07 09:21 PM
05/16/07 09:21 PM
Admin  Offline
OP
Administrator
Member
Joined: Oct 2000
Posts: 3,545
NY, USA
Quote
We often get calls to check switchboards that have had arcing faults and have insulators covered in carbon. Quite often electricians will tell us that they checked the bus with their ohm meter and all was clear. We try to tell them not to re-energize the board till the switchboard has been properly meggered either by us or I will supply a number for a firm that can perform the test (other than us) as sometimes electrical contractors think this HOO DOO VOO DOO we do is all about trying to separate them from their money and in these cases while money is an issue, my concern is their safety.

The test shown below was completed at 1000 VDC utilizing a megger, the carbon is pencil lead. The paper is a good insulator (meggered in the Gigaohms range) till it was contaminated with the pencil lead. The same test completed with an ohm meter showed no problems reading were acceptable. The difference is a 9 VDC ohm meter VS a 1000VDC megger.

- - BGaquin (Brian)

[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]

Tools for Electricians:
Re: Carbon Test [Re: Admin] #163787
05/17/07 03:55 AM
05/17/07 03:55 AM
J
johno12345  Offline
Member
Joined: Sep 2005
Posts: 97
United Kingdom
Thats quite an impressive demonstration. I think I will sort out the cleaning of our switchgear now! it is full of grinding dust and smoke. I guess that under the right conditions, it could explode!


I took my time, I hurried up, The choice was mine, I didn't think enough
Re: Carbon Test [Re: johno12345] #163789
05/17/07 07:44 AM
05/17/07 07:44 AM
R
RODALCO  Offline
Member
Joined: Dec 2005
Posts: 857
Titirangi, Akld, New Zealand
Very interesting test you have done there Brian.

Exactly what you show there is what happens in the real world.

I deal a lot with intermittend HT faults on 11 kV transformers. Dirty bushings cause a flasover, blow HT fuse. I always insist that the line crews disconnect the 11 kV cables prior to do an insulation test on the cable because of that reason.

I will do a similar test with a 5 kV megger, to show some of our fault staff why cables and bushings have to be clean.

Thanks for those great photo's

Regards, Raymond


The product of rotation, excitation and flux produces electricty.

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Joe Tedesco
Joe Tedesco
Boston, Massachusetts USA
Posts: 2,749
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
255,196 Are you busy
191,270 Re: Forum
181,032 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 15 (0.004s) Memory: 0.9534 MB (Peak: 1.0777 MB) Zlib enabled. Server Time: 2019-05-25 10:05:27 UTC