has anybody tried this? #163683 05/14/07 04:42 PM
Joined: Aug 2006
Posts: 356
Niko Offline OP
Member
Hi Folks,
Do you know if a OC (occupancy sensor) can be in series with a dimmer.
Here is what i am proposing to do:
Install two lowvoltage recessed cans above a indoor jacuzzi tub, have a dimmer control them and to comply with title 24, have the OC control the dimmer.

Has anybody tried this?

Thanks for your input


Be kind to your neighbor, he knows where you live

Work Gear for Electricians and the Trades
Re: has anybody tried this? [Re: Niko] #163686 05/14/07 05:34 PM
Joined: Feb 2007
Posts: 20
J
joncon Offline
Junior Member
As long as the OS is before the dimmer, no problem.

Re: has anybody tried this? [Re: Niko] #163687 05/14/07 05:37 PM
Joined: Jun 2005
Posts: 821
S
ShockMe77 Offline
Member
A guess:

If the occupancy sensor is rated for a particuliar voltage, then it will not be operating at it's rated voltage and therefore in violation of 110.3 (B).


Re: has anybody tried this? [Re: Niko] #163691 05/14/07 08:37 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
I particularly like to use Meastro dimmers for this! They make a neat effect as they fade up to the pre-set if left on. (only using the VC to control it) With a few dimmers you can kind of make a 'scene' out of it when operating the "Vacancy Sensor", (Not 'occupancy sensor'!) and all the dimmers come up to preset levels.

Shockme, VC uses NC contacts, the dimmer gets the same voltage, you dont or should not dimm the VC.


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: has anybody tried this? [Re: e57] #163692 05/14/07 08:43 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
I think I want to dub that the "Poor-mans Grafik Eye"....


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: has anybody tried this? [Re: e57] #163701 05/15/07 08:02 AM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
Should I mention that you should check also to see if your Code allows lights above the tub before you get too far along?

I know that Chicago is dead set against it.


Ghost307
Re: has anybody tried this? [Re: ghost307] #163717 05/15/07 01:00 PM
Joined: Oct 2002
Posts: 482
Z
Zapped Offline
Member
I don't see any problem with this approach. As long as the sensor is BEFORE the dimmer, all components are getting proper operating voltage.

BTW, I did not know that about Chicago Ghost. Do they also not allow sealed-trim can lights above showers?

Re: has anybody tried this? [Re: Zapped] #163718 05/15/07 02:03 PM
Joined: Dec 2002
Posts: 204
G
geoff in UK Offline
Member
Depends if its the type of PIR occupancy sensor which has its own neutral, or the type which is in series with the line and relies on that to power it. The former will work; the latter not.

Re: has anybody tried this? [Re: geoff in UK] #163719 05/15/07 02:29 PM
Joined: May 2005
Posts: 984
G
ghost307 Offline
Member
The wording in the Code is similar to NEC for pendant lights, but there's a part that prohibits many of the light installations of this variety by a somewhat left-handed means. It limits the mounting height to no lower than a minimum of 7 ft 6 in. above the maximum water level. Even then they require a ground-fault circuit interrupter for it.

You can use recessed fixtures with a glass or plastic lens and nonmetallic or electrically isolated metal trim, suitable for use in damp locations or surface-mounted fixtures with a glass or plastic globe and a nonmetallic body or a metallic body isolated from contact if the fixtures are suitable for use in damp locations lower than the 7'-6 above the maximum water level if you provide a ground-fault circuit interrupter.

To paraphrase the Chicago Code; "sure it's okay...just jump through this moving hoop while whistling Dixie and juggling these oranges".

They're very accomodating here.


Ghost307
Re: has anybody tried this? [Re: ghost307] #163722 05/15/07 04:49 PM
Joined: Aug 2006
Posts: 356
Niko Offline OP
Member
Thanks for all of your replies.

Mark, what is the difference between OS (occupancy sensor) and VS (vacancy Sensor)

Thanks


Be kind to your neighbor, he knows where you live

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CharlieE
CharlieE
Indianapolis
Posts: 201
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
MCosta 3
Popular Topics(Views)
275,442 Are you busy
209,344 Re: Forum
196,623 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3