Fusible safety switch for Air Compressor #163567 05/10/07 07:02 PM
Joined: Jan 2006
Posts: 8
I
ih17dka8 Offline OP
Junior Member
If Air Compressor is used only for blowing dust off in factory, do we need to install a FUSIBLE safety switch within sight of air compressor?

If so, would you refer to the NEC verse?

And How about in case of air conditioning compressor?

I mean I think I can install non-fusible safety switch for the disconnecting means for air compressor or air conditioning compressor.

After all this compressor circuit is connected to inverse circuit breaker in remote electrical room which provide overcurrent protection.

2017 / 2014 NEC & Related Books and Study Guides
Re: Fusible safety switch for Air Compressor [Re: ih17dka8] #163570 05/10/07 08:04 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
The requirement to fuse is found in the manufacturer's instructions for that specific piece of equipment. Still, that only means that there has to be a fuse somewhere in the circuit.
If the nameplate reads "fuse," rather than "overload device (or some such), then a fuse is needed; a breaker is not sufficient.

Otherwise, the disconnect has to be mounted as the code calls. There is no rule against having more than one disconnect; many times I have seen the fused disconnects at the control center, while there was a second disconnect mounted right at the equipment.

Re: Fusible safety switch for Air Compressor [Re: renosteinke] #163575 05/10/07 09:45 PM
Joined: Aug 2006
Posts: 21
S
ScubaDan Offline
Member
Hi all,

"within sight of air compressor"

As I remember, it must be within 3 feet of the device.

And usually the panel board will contain the air compressors "Primary Protection" rated at 125% of the FLA and the fused disconnect, "Secondary Protection" will be rated anywhere from 175% to 250% or higher per NEC 430 something depending on the fuse characteristics.

I'd like to add that using a MCCB as the primary protection with a fuse (in place of another MCCB) for the secondary protection offers the best combination of protection against both short circuit and arc flash serneros.

Re: Fusible safety switch for Air Compressor [Re: ScubaDan] #163586 05/11/07 10:09 AM
Joined: Nov 2006
Posts: 348
I
ITO Offline
Member
LOL…. Yeah had that 3’ argument with an engineer one time.

Take a look Article 100 Definitions:
In Site From (Within Site From, Within Site)

It’s 50 foot.


101° Rx = + /_\
Re: Fusible safety switch for Air Compressor [Re: ITO] #163595 05/11/07 07:36 PM
Joined: Aug 2006
Posts: 21
S
ScubaDan Offline
Member
Well, I was working off of memory...and I'm an engineer...

Wow, I really fell into this one.

I guess that you should also clarify "insight" as being no more than 50 feet. (oops - I re-read your post and noticed that you had already stated this - sorry).

And...being from the industrial world for almost 30 years, if it isn't close to the machine most maintainence personal will try to work without disconnecting the machine. That's why we always try to maintain the distance to around 3 feet or a step or two away.

Last edited by ScubaDan; 05/11/07 07:37 PM.
Re: Fusible safety switch for Air Compressor [Re: ScubaDan] #163613 05/12/07 09:10 AM
Joined: Nov 2006
Posts: 348
I
ITO Offline
Member
Considering the code reads like it was written by a bunch of lawyers and gets re-written every few years by industry insiders it no surprise that we all miss a subtlety of the code every now and then. My favorite debate is the whole “minimum voltage drop is not a code requirement, it’s just a recommendation”.

Sure 3ft is a good design and as an engineer you can put that on the plans as part of the scope, the code should be read as a minimum requirement for a reasonably safe installation, and why design to minimum requirements?


101° Rx = + /_\
Re: Fusible safety switch for Air Compressor [Re: ITO] #163622 05/12/07 02:04 PM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Offline
Member
I wouldn't want to see any short distance, like 3', we have enough trouble keeping disconnects 110.26 compliant as it is. As long as they are truly within site and convenient for the maintainer so they will actually get used, I am happy.


Greg Fretwell
Re: Fusible safety switch for Air Compressor [Re: ih17dka8] #163626 05/12/07 02:42 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
I can't think of a better example of where the NEC is a 'safety minimum,' rather than a design manual, instruction manual, etc. This topic also highlights the trouble with 'one size fits all' solutions.

When it comes to disconnects, I like to begin with "forget about the code..."

Under what circumstances will you want to disconnect the thing? And, where will you be when that happens?

It makes sense to be able to disconnect something from the control room.
It makes sense for things that need checking ... such as fuses ... to be placed where they are easily accessible.
It also makes sense that the guy working on the thing be able to surely disconnect it, right there ... and that there be no possibility of grabbing the wrong disconnect.

If I was changing a motor, I'd want a switch right at the end of the flex that feeds it. Indeed, a cord & plug would be even better.

If I were needing to disconnect the next Chernobyl, I'd want the disco located somewhere, say, 25 miles upwind.

I sure an heck don't want to have to climb on a roof, in the rain, to check the fuses, or push the starter reset. Yet, few things are more discouraging than a wall of unmarked switches, with everything disappearing into a gutter.

Re: Fusible safety switch for Air Compressor [Re: renosteinke] #163627 05/12/07 06:25 PM
Joined: Jul 2004
Posts: 9,571
G
gfretwell Offline
Member
I know what you mean Reno. One of my few red tags was a 2000 sqft equipment rooms with all the disconnects neatly grouped by the door. I told the installer to go take the covers off one of the 480v air handlers at the far end, start poking around in the wiring box and I will call "maintenance" to complain about my AC not working. Maintenance man opens the door and says "here's your problem".

They got the point. In fact what we got was an additional disconnect at each machine.
They were thinking the disconnect was for firemen entering the room to fight a fire. I pointed out you are also protecting the people who maintain the boxes.
I also got another entrance to the room. (actually a tall attic)
It is amazing what engineers can come up with when they get on board. They found a "pull down" attic ladder that was class 1 and handled a 14' ceiling. It may have actually been custom built. Very slick.


Greg Fretwell
Re: Fusible safety switch for Air Compressor [Re: gfretwell] #163633 05/12/07 10:44 PM
Joined: Nov 2006
Posts: 348
I
ITO Offline
Member
Not sure what a “thing” is...

From experience, many service calls, callbacks, and even a few consulting gigs, I feel very comfortable saying that maintenance men are dangerous and we professionals should make damn sure they know how to turn it off before they start beating it with a hammer.

Fuses are a good thing, they cost money and even the dumbest of maintenace men will think twice after burning up the second set...


101° Rx = + /_\
Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
275,645 Are you busy
209,569 Re: Forum
196,923 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3