B
Member
I've been asked to phase a 3-phase motor. I'm not sure if this is normally the electrician's job or the HVAC's. What type of meter do I need and what is the process?

Thanks,
Byron

Joined: Feb 2003
Posts: 231
R
Member
Question-

Do you just have to do a rotation test?

or

Do you have this 3 phase motor and all of the winding connections are all apart and you need to connect them up?

Joined: Sep 2003
Posts: 114
B
Member
Rotation test only.

Joined: Feb 2003
Posts: 231
R
Member
If its for a piece of equipment that won't mind it going the wrong way for a short time then I would just do the 50/50 test. If you find it going the wrong direction just change it. No meters required just eyes.


Joined: Sep 2003
Posts: 114
B
Member
But... if I want to meter it and have it going the right way to begin with?


Joined: Sep 2005
Posts: 421
Member
there are two types of phase rotation meters one requires line voltage to operate and the other is self-powered to check motors that are unwired...or going back into service

you use the powered type by connecting the three meter leads to your source voltage usually at the equipments last termination such as a starter or disconnect to verify your incoming voltage...and if you have an arrow on the motor..you then connect the motor leads 1,2,3, for the correct rotation..which as I recall is CCW opposite the shaft end

if you want to check a dead motor and can turn the shaft, use the self-powered type ...again connecting the meter leads to the motor leads and turn the shaft

several are available from Fluke, AEMC, Knopp,....
and Ideal makes a multimeter that you can use




Tom
Joined: Sep 2005
Posts: 421
Member
BTW, in my opinion the Fluke is overpriced at almost $200.00

the AEMC PMR-2 is the most economical, <<<<I own this one

while the Knopp is the most rugged and has been around a long time


Tom
Joined: Sep 2005
Posts: 421
Member
and there are several to choose from right here at the ECN Store
https://www.electrical-contractor.net/The_Store/EX/480300_303.htm

Last edited by togol; 05/01/07 09:48 PM. Reason: spelling

Tom

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Top Posters(30 Days)
triple 3
BigB 3
Popular Topics(Views)
303,205 Are you busy
232,202 Re: Forum
216,945 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5