#16281 11/08/02 09:24 PM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Is a switch for a recessed light in a residential home shower required to be 5 ft away?


The Golden Rule - "The man with the gold makes the rule"
#16282 11/08/02 10:15 PM
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
Nope. There are no requirements for switches pertaining to shower spaces.
(That I'm aware of)
</going out on a limb>


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
#16283 11/08/02 11:21 PM
Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
Allow me to correct myself...

404.4 pertains to switches in wet locations, including shower stalls.

What I meant to say was: Nope. There are no requirements for switches pertaining to any specific distance to shower stalls. They however, cannot be installed within the stall unless installed as a part of a listed shower assembly.

(Thanks, Joe!)

[Linked Image]



[This message has been edited by sparky66wv (edited 11-08-2002).]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
#16284 11/08/02 11:53 PM
Joined: Jul 2002
Posts: 74
S
Member
Here if the switch is within 6' they must be grnd. fault protected. 3' or less, it is not permited at all. I have always wondered.. can gets enough steam, gfi. trips. Then you are left in the shower with no light. That to me seems more dangerous.
John

#16285 11/09/02 01:20 AM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Good point scjohn, I was thinking the same thing earlier today.


The Golden Rule - "The man with the gold makes the rule"
#16286 11/09/02 01:34 AM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
For a spa or hot tub Art 680-40(3)(c) says wall switches must be 5ft from the inside edge, but I could not find anything on shower switch locations.


The Golden Rule - "The man with the gold makes the rule"