Joined: Nov 2006
Posts: 1
F
fredc Offline OP
Junior Member
Hey I was wondering if someone could help me figure out what size wire I need to use. It is a 2 family house has 2 sub panels 200amps each. I am putting a 2 gang stackable meter pan. I am use to single family house where everything is straight forward. The problem is these apartments are small only 900sf each. The 200 amp panels are an over kill. Could someone help me out here?

Joined: Jul 2004
Posts: 9,667
Likes: 6
G
Member
You have to serve 200a if that is the breaker you have. 4/0 al to each and 600kcmil (or parallel 4/0) to the service point, the way I see it. The PoCo will probably connect that to a 2ga al triplex drop.


Greg Fretwell

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
timmp
timmp
Leo, IN, USA
Posts: 28
Joined: June 2004
Top Posters(30 Days)
dsk 6
Popular Topics(Views)
284,726 Are you busy
217,350 Re: Forum
203,701 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5