Residential 2 apartment load calcs. #162141
04/13/07 06:22 PM
04/13/07 06:22 PM
fredc  Offline OP
Junior Member
Joined: Nov 2006
Posts: 1
freehold NJ
Hey I was wondering if someone could help me figure out what size wire I need to use. It is a 2 family house has 2 sub panels 200amps each. I am putting a 2 gang stackable meter pan. I am use to single family house where everything is straight forward. The problem is these apartments are small only 900sf each. The 200 amp panels are an over kill. Could someone help me out here?

Work Gear for Electricians and the Trades
Re: Residential 2 apartment load calcs. [Re: fredc] #162151
04/13/07 09:12 PM
04/13/07 09:12 PM
gfretwell  Offline

Joined: Jul 2004
Posts: 9,186
You have to serve 200a if that is the breaker you have. 4/0 al to each and 600kcmil (or parallel 4/0) to the service point, the way I see it. The PoCo will probably connect that to a 2ga al triplex drop.

Greg Fretwell


2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman


Member Spotlight
Posts: 70
Joined: June 2012
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 5
Admin 5
Popular Topics(Views)
244,858 Are you busy
181,977 Re: Forum
172,013 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 15 (0.005s) Memory: 0.9425 MB (Peak: 1.0603 MB) Zlib enabled. Server Time: 2018-03-22 23:02:42 UTC