photo cell 208v
#161537
04/04/07 02:38 AM
|
Joined: Aug 2001
Posts: 545
OP
Member
|
Is it legal to install a 208v photo cell so it switches one side of the 2 phases? I would think running it through a 2 or 4 pole contactor to switch both sides would be better. I found one done this way and think they had trouble with it, (not to mention that one side would still be hot if you were working on it). It was for some parking lot lights. I put a contactor controlled by a photo cell on it.
The Golden Rule - "The man with the gold makes the rule"
|
|
|
Re: photo cell 208v
[Re: aldav53]
#161562
04/04/07 11:38 AM
|
Joined: Jul 2004
Posts: 9,575
Member
|
410.48 and 410.54 seem to support that view
Greg Fretwell
|
|
|
Re: photo cell 208v
[Re: gfretwell]
#161566
04/04/07 12:34 PM
|
Joined: Jan 2004
Posts: 1,507
Member
|
Good Call Greg. I learned something today.
George Little
|
|
|
Re: photo cell 208v
[Re: George Little]
#161568
04/04/07 01:02 PM
|
Joined: Sep 2006
Posts: 58
Member
|
Yeah, Greg. I tried to find a way to get around opening both legs and even went to some photocell manufactures sites. Looks like aldav53 is correct.
|
|
|
Re: photo cell 208v
[Re: yanici]
#161576
04/04/07 03:54 PM
|
Joined: Jul 2004
Posts: 9,575
Member
|
My first guess was it might be OK if you had a 2 pole disconnect in front of the photocell but I don't see the language that supports it. I know you can have some types of equipment that allow this for control only (with a real disconnect present) but "lamp holders" and ED lighting does not seem to be included. If the installation was such that it was clear that the future maintainer could relamp safely I might be softer on this ruling.
Greg Fretwell
|
|
|
Re: photo cell 208v
[Re: gfretwell]
#161616
04/05/07 08:09 AM
|
Joined: Jan 2001
Posts: 1,044
Member
|
I've seen plenty of HPS & Metal Halide floods & wallpacks that were supplied by 208 volt or 240 branch circuits and were individually controlled by a photocell. Since these fixtures came from the factory that way and are UL listed, I think the second paragraph of 90.7 would allow a factory installed photocell to switch just one energized conductor.
Of course, if you're the AHJ, it is up to you to approve equipment, listed or not.110.2
Few things are harder to put up with than the annoyance of a good example.
|
|
|
Re: photo cell 208v
[Re: Tom]
#161626
04/05/07 11:56 AM
|
Joined: Jul 2004
Posts: 9,575
Member
|
A lot of things go on inside listed products that we would not allow in field assembled equipment. I suppose it would really come down to your AHJ's definition of "switching device". If you called the PC something else and there was a real 2 pole switch present for safe relamping, I would not be all that concerned.
Greg Fretwell
|
|
|
|
|