Hi folks,
I will be installing a new meter main and am using the existing meter main as a sub panel. Besides the obvious separate the grounding bar from the neutral bar, install a new GEC from the new panel, can the existing meter location be covered with a clear cover? Or the existing metermain be replaced with a regular subpanel?
Does the NEC address this or it a local AHJ decision?

Thank you
Edward


Be kind to your neighbor, he knows where you live

2017 / 2014 NEC & Related Books and Study Guides
Re: meter main as sub [Re: Niko] #161067
03/29/07 08:54 PM
03/29/07 08:54 PM
Niko  Offline OP
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
Either you reach a higher point today, or you exercise your strenght in order to be able to climb higher tomorrow.
Friedrich Nietzsche

Last edited by Niko; 03/29/07 08:55 PM. Reason: i tried to add as a signature.but went in as a reply

Be kind to your neighbor, he knows where you live

Re: meter main as sub [Re: Niko] #161193
03/31/07 10:36 AM
03/31/07 10:36 AM
A
Alan Nadon  Offline
Member
Joined: Mar 2005
Posts: 399
Elkhart, IN. USA
Neutral (grounded conductor) will be bonded in the old meter socket. As an inspector I would not allow it.
Alan--


Alan--
If it was easy, anyone could do it.
Re: meter main as sub [Re: Alan Nadon] #161199
03/31/07 11:00 AM
03/31/07 11:00 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,323
Estero,Fl,usa
I assume he is saying he will bypass or remove the meter connections and only use the disconnect with the cabinet as a J box. If he can isolate the bonding that should not be an issue but I still would question the suitability of the cover with nothing but that plastic "snap in" over the meter hole. They tend to fall apart pretty fast in the sun. If you screwed a metal cover over the hole I would not be too concerned.


Greg Fretwell
Re: meter main as sub [Re: Niko] #161217
03/31/07 02:33 PM
03/31/07 02:33 PM
Niko  Offline OP
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
Thank you for the replies,
Alan, i will isolate (unbond) the grounding and the grounded.
My only concern is the meter location and as suggested i may install a metal cover VS clear plastic.

Thanks again for the replies.


Be kind to your neighbor, he knows where you live


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
252,206 Are you busy
189,182 Re: Forum
178,861 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.025s Queries: 15 (0.004s) Memory: 0.9688 MB (Peak: 1.1106 MB) Zlib enabled. Server Time: 2018-12-15 02:14:10 UTC