#160703 - 03/24/07 05:41 PM 3 Phase 480 parallel runs.....  
Grover  Offline
Member
Joined: Jan 2005
Posts: 109
Sebago, ME, USA
I've posted about this before, but a new twist.

Spec'd out; pipe on site, ready to dig and bury. Customer wants to increase amperage - future capacity. Loads are all motors - 2 soft start.

Spec'd at 1290A - 3 parallel 4" RMC runs, each containg A,B,C,N,G - 500 MCM Cu + 1 3/0 G.

He now wants 1600A. My solution: 4th pipe run - give me 1720A; he wants to add wire to the planned 3 runs.

Fill factor is ok to add 4th wire, but it would lead to A,A,B,C,N in pipe 1, A,B,B,C,N in pipe 2 and so on. I was always taught (in RMC)to keep A,B,C,N together in each pipe, or you end up with a "shorted turn" effect due to any imbalance, and heat up the pipe.

All I can find in a first look is Article 300.20 - "all phase conductors shall be grouped together".

Advice? Comments? Analysis? Pointers?

Thanks!


Work Gear for Electricians and the Trades

#160705 - 03/24/07 06:23 PM Re: 3 Phase 480 parallel runs..... [Re: Grover]  
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
You shouldnt have any induction problems as all the phases and neutral are present in each conduit. You should make sure the paralleled conductors are hte same length and size. Also, why not use the RMC as the ground?


#160708 - 03/24/07 06:49 PM Re: 3 Phase 480 parallel runs..... [Re: Grover]  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
You cannot run the conductors like that. It is a violation of 310.4 and will produce excessive heat. Also you don't have enough copper with 3 runs of 500kcmil for 1290 amps...that is only good for 1140 amps. You have to use the 75° column for this application unless all of the terminations are listed for 90°....very unlikely.
Don


#160710 - 03/24/07 06:57 PM Re: 3 Phase 480 parallel runs..... [Re: resqcapt19]  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
You could make it work for 1600 amps with 8 350 kcmil in each raceway, assuming that the grounded conductor is not required to be counted as a current carrying conductor. The 90° ampacity of 350 is 350 amps and we can use that for purpose of derating. The derated ampacity would be 280 amps and 6 conductors at 280 gives you a total ampacity of 1680 amps. Ten 350 kcmil THWN-2 will fit in the 4" rigid so you will have room for the EGC. Note that it will have to be a 4/0 for each raceway.
Don


#160728 - 03/25/07 06:14 AM Re: 3 Phase 480 parallel runs..... [Re: resqcapt19]  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
I agree with both of Don's posts.

I do have a question, do you need an EGC at all?

You did not say if this was a service or a feeder. If it's a service you can, and should drop the EGC from the plan.

Last edited by iwire; 03/25/07 06:14 AM.

Bob Badger
Construction & Maintenance Electrician
Massachusetts

#160830 - 03/26/07 03:06 PM Re: 3 Phase 480 parallel runs..... [Re: iwire]  
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
why would there be any heat from induction with all the phases present?


#160835 - 03/26/07 05:10 PM Re: 3 Phase 480 parallel runs..... [Re: trekkie76]  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
trekkie,
Quote
why would there be any heat from induction with all the phases present?

You have more than just all phases in each conduit...you have an extra conductor from a single phase with no conductors of the other phases to cancel the fields. This would be the same as putting A in one conduit and B in another conduit. Remember this is a ferrous metal conduit. If the conduit was non-ferrous, you would not have the heating problem, but there still would be a violation of 310.4.


Don(resqcapt19)

#160869 - 03/27/07 05:22 AM Re: 3 Phase 480 parallel runs..... [Re: resqcapt19]  
Grover  Offline
Member
Joined: Jan 2005
Posts: 109
Sebago, ME, USA
Thanks for all the input & comments gang.

Everything is in a state of "flux" <grin> with the customer right now..... cost vs. extra/future capacity....

Grov


#160893 - 03/27/07 12:01 PM Re: 3 Phase 480 parallel runs..... [Re: Grover]  
trekkie76  Offline
Member
Joined: Jun 2004
Posts: 220
baileyville, maine, usa
yes but it is the A phase from the same system, which has the B,C,and N in the conduit. How would they not cancel out the magnetic effects in the condiut?


#160894 - 03/27/07 12:08 PM Re: 3 Phase 480 parallel runs..... [Re: trekkie76]  
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
ASSume you have 100 Amps per phase CONDUCTOR. That will give 200 A phase A flux (2 conductors), 100 A phase B flux, 100 A phase C flux. The flux due to 100 Amps of A + B + C will cancel, but you still have an EXTRA 100 A of phase A flux. There is no more phase B or C flux to cancel it out.


Hello Hot pipe.



Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 15 (0.003s) Memory: 0.8116 MB (Peak: 0.9901 MB) Zlib enabled. Server Time: 2017-12-14 07:55:24 UTC