ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
IRC M1307.3
by gfretwell. 08/18/18 09:08 AM
Light Pole Grounding
by Mosfet74. 08/18/18 08:42 AM
Calling all Non-US members!! (Non-US only)
by Bill Addiss. 08/13/18 05:52 PM
Upgrade the old panel
by gfretwell. 08/13/18 12:20 AM
depth of duckbank
by ghost307. 08/12/18 09:26 PM
New in the Gallery:
Plug terminals
Housebilding DIY wiring
Who's Online Now
1 registered members (gfretwell), 7 guests, and 18 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
Low voltage wiring in High voltage trench #160436
04/04/06 07:10 PM
04/04/06 07:10 PM
H
hdtvluvr  Offline OP
Junior Member
Joined: Apr 2006
Posts: 4
Tennessee
I need to have some Cat5e and RG6 cables installed. It is in a location that will require them to be installed outside. I am having 2 new 220V circuits added (one for a well pump) and was told by my electrical contractor that the same ditch could be used for the low voltage stuff as long as they were in a separate conduit and separated with 6 - 12 inches of dirt.

The 220v circuits will be in their own PVC conduit 24 inches down. Will the 2 conduits and approx. 12 inches of dirt be sufficient to prevent interference in the low voltage wiring? Thanks!

Study Guides for VDV / Structured Cabling Installers

Voice, Data, Video, (VDV) Fiber Optics, Communications, Low Voltage,
Fire Alarm, Electronic Security Systems Installations & Related

NTC Low Voltage Training & NICET Exam Study Guides
Low Voltage Training & NICET Exam Study Guides

Re: Low voltage wiring in High voltage trench #160437
04/04/06 10:00 PM
04/04/06 10:00 PM
G
gfretwell  Online Content

Member
Joined: Jul 2004
Posts: 9,252
Estero,Fl,usa
More than enough. If you had them duct taped together you wouldn't see any interferance between 60hz and CAT 5. The raceways provide electrical separation too.

The main reason for separating buried utilities is so one guy can dig his stuff up without whacking the other guy's stuff.

[This message has been edited by gfretwell (edited 04-04-2006).]


Greg Fretwell
Re: Low voltage wiring in High voltage trench #160438
04/04/06 10:14 PM
04/04/06 10:14 PM
J
JoeTestingEngr  Offline
Member
Joined: Nov 2005
Posts: 794
Chicago, Il.
Frankly, I don't see an issue with induced noise from the 220 ckts. I might see a hum issue depending on what you're planning to have on both ends of the RG-6. If you are running baseband composite video, which I doubt, you might find yourself in need of an EQ DA. The EQ DAs have a differential input as opposed to a single ended or unbalanced input for the non-EQ DAs.
Joe

Re: Low voltage wiring in High voltage trench #160439
04/05/06 01:04 PM
04/05/06 01:04 PM
H
hbiss  Offline
Member
Joined: Dec 2003
Posts: 886
Hawthorne, NY USA
When I worked for cable the companies doind subdivisions and developments we put coax in the same trench with 12.5kv primaries. Trench was 36" wide, primary on one side, 120/240v services in the middle, our stuff on the other.

-Hal

Re: Low voltage wiring in High voltage trench #160440
04/05/06 02:46 PM
04/05/06 02:46 PM
H
hdtvluvr  Offline OP
Junior Member
Joined: Apr 2006
Posts: 4
Tennessee
Thanks for everyone's help.

Joe
I'll be using the RG6 for DirecTV and/or Cable feeds (up to 2.5 GHz). Is this baseband video?

Re: Low voltage wiring in High voltage trench #160441
04/05/06 05:49 PM
04/05/06 05:49 PM
J
JoeTestingEngr  Offline
Member
Joined: Nov 2005
Posts: 794
Chicago, Il.
You are fine then because you are dealing with RF. Imagine hooking one end of the RG6 through a phono plug adapter to your VCR video output. Then imagine hooking the other end into the video 1 input of your neighbor's TV/monitor, three houses down. It would be quite likely that you would see a nasty bar traveling up through the picture. That's because there could be a sine wave on both center and outer conductor, when viewed from the receiving end. A differential amplifier will cancel most of that out because it is "common mode" hum. A single ended or unbalanced amplifier will faithfully reproduce the hum with the video.
Joe

Re: Low voltage wiring in High voltage trench #160442
04/06/06 08:45 PM
04/06/06 08:45 PM
T
techie  Offline
Member
Joined: May 2005
Posts: 247
palo alto, ca usa
Make sure that you are using cable designed for underwater use. as you can assume that any underground conduit will be flooded at least some of the time, if not most of the time.

Re: Low voltage wiring in High voltage trench #160443
04/07/06 12:27 PM
04/07/06 12:27 PM
H
hdtvluvr  Offline OP
Junior Member
Joined: Apr 2006
Posts: 4
Tennessee
>>Make sure that you are using cable designed for underwater use.<<

The cat5e cable I have is just standard cable. My RG6 may actually be RG6/U but I'll have to check. I've never seen any Cat 5e for underwater use. If I glue all of the joints on the PVC conduit, why should I expect it to be flooded some if not most of the time? I assumed the PVC would be water tight like it is for water lines.

Re: Low voltage wiring in High voltage trench #160444
04/07/06 12:46 PM
04/07/06 12:46 PM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
A wet location is defined by the NEC as "installations underground ..."


Ron
Re: Low voltage wiring in High voltage trench #160445
04/07/06 12:50 PM
04/07/06 12:50 PM
H
hbiss  Offline
Member
Joined: Dec 2003
Posts: 886
Hawthorne, NY USA
The "U" in RG-6/U does not stand for Underground. [Linked Image]

-Hal

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 68
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
248,618 Are you busy
186,361 Re: Forum
175,819 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 15 (0.004s) Memory: 1.0283 MB (Peak: 1.1997 MB) Zlib enabled. Server Time: 2018-08-19 04:27:55 UTC