is running cat5e in heating ducts alowed ?


Dryden
Study Guides for VDV / Structured Cabling Installers

Voice, Data, Video, (VDV) Fiber Optics, Communications, Low Voltage,
Fire Alarm, Electronic Security Systems Installations & Related

NTC Low Voltage Training & NICET Exam Study Guides
Low Voltage Training & NICET Exam Study Guides

Re: running cat5e #159800 01/30/05 06:12 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
Simple answer: No
Little more specific: you can go THROUGH, at ninety degrees. I would infer that cable should then be plenum rated.

Re: running cat5e #159801 01/30/05 07:28 PM
Joined: Nov 2004
Posts: 11
D
dryden_burton Offline OP
Member
i didnt think so
ok thanks


Dryden
Re: running cat5e #159802 02/01/05 05:18 PM
Joined: Dec 2004
Posts: 23
D
dstanford Offline
Member
i don't think you can run through ducts even at 90 degrees... where did you see that at renosteinke. why that would be something to take a picture of and submit to the picture forum

Re: running cat5e #159803 02/01/05 08:47 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Not that its a great practice, it is allowed with some limitation. (With Plenum rated cable...)

Quote
800.53 (A)Plenum. Cables installed in ducts, plenums, and other spaces used for environmental air shall be Type CMP. Abandoned cables shall not be permitted to remain. Types CMP, CMR, CMG, CM, and CMX and communications wire installed in compliance with 300.22 shall be permitted. Listed plenum communications raceways shall be permitted to be installed in ducts and plenums as described in 300.22(B) and in other spaces used for environmental air as described in 300.22(C). Only Type CMP cable shall be permitted to be installed in these raceways.


Mark Heller
"Well - I oughta....." -Jackie Gleason
Re: running cat5e #159804 02/01/05 09:15 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
Looks like I get smacked for "shooting from the lip." Apparently I was repeating something I'd heard, rather than actual code. Of course, you must forgive me, as I've never seen wiring in ducts (other than a short length to power something that was part of the duct system!).
300.21 and .22 seem to be the primary place where the NEC discusses wiring in ducts, with numerous other sections that boil down to "OK to run plenum rated wires in ducts." There ARE some other qualifications, so check it out.

Re: running cat5e #159805 02/01/05 09:25 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Reno, I'm not smacking anyone....

It is a horrible practice in my opinion though. I've seen it done, even been forced by an employer to do it myself once. I don't like it at all.

Seen this thread for a day or so, but was reluctant to answer. Wish it were not an actual code.

[This message has been edited by e57 (edited 02-01-2005).]


Mark Heller
"Well - I oughta....." -Jackie Gleason

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,016 Are you busy
205,012 Re: Forum
193,127 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3