M
Member
I've worked in a few houses, all built in the '80s that had the furnace in the garage. Typically, the return air would enter through a built plenum benaeth the unit, and there would be ducting abouve it going back into the house. My question is this: if the house requires 1 hour seperation from the garage, why were there no fire actuated dampers on the return and supply of these furnaces? Was the one hour seperation not required back then? Is there an exception for residences?

BTW, these were all located in southern California.

Thanks,
mike

Latest Labor & Material Cost Estimating Guides

Latest Labor and Material Cost Estimating Guides

Joined: Jul 2004
Posts: 10,041
Likes: 37
G
Member
I suppose it depends on what code you are on but the "1 hour" fire rating usually only applies to dwelling space above a garage.
I have asked about fire dampers myself and that is what I hear. They use garden variety hollow core passage doors between the garage and mud room or laundry room here in Florida.


Greg Fretwell
Joined: Feb 2003
Posts: 67
P
Member
mike,
302.4 exc#3 of the calif bldg. code(1997 u.b.c.)states no damper required if ducts are 26 guage and no openings in the garage.

Joined: Oct 2004
Posts: 132
M
Member
pwood,
I don't have the building code so let me ask some more questions:
-if the ducts are thicker than 26 gauge, is that OK?
-By no openings, do you mean that there are nor registers in the garage?

Thanks,
Mike

Joined: Feb 2003
Posts: 67
P
Member
mike,
the 26 guage is a minimum thickness and no openings are allowed in the garage.no registers or returns,only the unit with supply and return directly to and from the house.