Joined: Apr 2005
Posts: 2
E
Junior Member
Is anyone aware of any code that limits how close a gas pipe may be to an electrical panel assuming that all working clearance requirements of NEC 110 are met? (It's in a hospital boiler room.)

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Aug 2003
Posts: 1,374
R
Moderator
You would have to know what gas code is adopted in your area. If it is the International Fuel Gas Code (IFGC), it is not addressed. If it is the NFPA 54, I'm not sure, as I have never read that document.


Ryan Jackson,
Salt Lake City
Joined: Jun 2003
Posts: 1,143
D
Member
Check with your local utilities as well - I know out PoCo (ComEd) lists a zone around the meter for gasworks in their handbook...

Joined: Mar 2001
Posts: 2,056
R
Member
NFPA 54 (Fuel Gas Code) Section 2.7.2(c)
requires that gas meters be located 3' from sources of ignition. Our PoCo requires electric meters be 3' away from gas meters.
But, I don't think that gas piping is an issue as long as the clearances from the electrical panel are observed.

Joined: Apr 2005
Posts: 2
E
Junior Member
Ok, thanks for your help!