I am bidding a job that includes installing Exit/Emergency Lighting in a hoagie shop. Does anyone have a link for spec-ing? Are they required in restrooms? Small ofice (6x6) within a larger office? Spacing fixtures along 40ft wall? Minium candle power? etc, etc
Regards, Jim
|
|
|
|
Joined: Apr 2002
Posts: 7,398 Likes: 7
Member
|
Jim: The UCC (5:23) has basic requirements for em/exit lighting.
Your local Fire Sub-Code is the guy to talk to as to exact locations.
Bathrooms are a 'tough' call, some twp want it, some seem to care less.
What about the job plans?? CH is probably a Class I town and should require sealed, signed drawings??
John
John
|
|
|
|
Joined: Dec 2001
Posts: 15
OP
Member
|
This job is in Philadelphia.
|
|
|
|
Joined: Aug 2004
Posts: 186
Member
|
Better check with the PFD, stop in at any local station and they will be more then willing to help you. I dont think philly does it yet but some towns are beging to require you to also install them at floor level. So that one can see them while crawling through the smoke. As a firefighter i am ALL for this. You will never see them at the top of the wall through the smoke of an average fire yet at all in a smokey one. Regardless check with the fd. Here i did some of the leg work for you this is the PFD web site; The contacts section. http://www.mfrconsultants.com/pfd/contact_info.shtml Good luck. [This message has been edited by NJ Wireman (edited 12-08-2004).] [This message has been edited by NJ Wireman (edited 12-08-2004).]
|
|
|
|
Joined: Apr 2002
Posts: 7,398 Likes: 7
Member
|
Coachman: Sorry your profile said NJ. Still, contact the Fire Official or Fire Dept.
BTW, welcome to the forums.
John
John
|
|
|
|
Joined: Jun 2004
Posts: 613
Member
|
Check in the Life Safty Code 101...chapter 7 covers emergency lighting and exit signs.
shortcircuit
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Generally speaking, emergancy lighting is required in spaces or buildings where two exits are required. That would mean bathrooms aren't reqiured. The emergancy lights must put out 1 foot candle at the floor level.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Jul 2005
Posts: 56
Member
|
coachman:
NFPA 101 Life Safety Code will answer all these questions for you.
|
|
|
|
Joined: Jun 2006
Posts: 110
Member
|
Firstly, let me say that I am only experienced in res. work, so commercial fire codes are out of my league. However, having an emergency light in the restrooms might be nice- wouldn't want to be on the can and have it go black. To me, that would be a tad unnerving.
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Firstly, let me say that I am only experienced in res. work, so commercial fire codes are out of my league. However, having an emergency light in the restrooms might be nice- wouldn't want to be on the can and have it go black. To me, that would be a tad unnerving. True...but not exactly an emergency, is it?