ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
New fan motor for Panasonic
by gfretwell. 06/21/19 10:56 AM
Burning out of return(white) side of 120volt rec
by crselectric. 06/14/19 02:15 AM
Video door bell causing chime activation of coil
by JoeTestingEngr. 06/13/19 12:43 PM
Troubleshooting Voltage Drop Across Relay
by gfretwell. 06/09/19 11:49 AM
Apple Recalls Three-Prong Wall Plug Adapters
by Admin. 06/05/19 09:06 PM
New in the Gallery:
What is this for?
Plug terminals
Who's Online Now
0 registered members (), 4 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
egress illumination #154219
10/01/04 08:52 PM
10/01/04 08:52 PM
J
jsherrard  Offline OP
Member
Joined: Jul 2004
Posts: 19
I need help with comments that a plan reviewer made about egress illumination in a commerial office building. He refered to the North Carolina Fire Prevention Code 1003.2.11 that says "The means of egress, including the exit discharge, shall be illuminated at all times the building space served by the means of egress is occupied." His comments indicate to satisfy this requirement there has to be either a wall switch and light at the egress or night-lighting. This is inside the building, not outside and is not related to the requirements for normal power, not emergency lighting. I have not had this requirement noted on plans before. Is anyone familiar with this interpetation? Are there other ways to satisfy this requirement?

Building Codes & Related References
Re: egress illumination #154220
10/02/04 05:34 PM
10/02/04 05:34 PM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
I'm not familiar with NC rules and regulations, but the reviewer is correct regarding the emergancy illumination. All portions of the means of egress that are large enough to require two exits (including outside at the exit discharge) are required to have emergancy illumination. I find the comments a little strange, but the way I always see this requirement satisfied is by placing emergancy lighting at the outside of the exit doors, and all other areas requiring the illumination.


Ryan Jackson,
Salt Lake City
Re: egress illumination #154221
10/28/04 08:08 PM
10/28/04 08:08 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
The exit discharge is the area outside the building, giving the fleeing occupants access all the way to a public way (street, parking lot or alley). In these larger buildings, this "night-light" is required to be lit at all times during darkness when the building is occupied, just the same as the EXIT lights and other egress lighting (night-lights or emergency lights) throughout the building.
A switched porch light would not qualify as this required egress lighting. A photo-cell or time-clock controlled porch light might fit the bill.
All egress and EXIT lighting needs to be on an emergency circuit, or have battery back-up power.


Earl

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 2
Khombo 2
Popular Topics(Views)
255,836 Are you busy
191,816 Re: Forum
181,580 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.023s Queries: 14 (0.005s) Memory: 0.9528 MB (Peak: 1.0762 MB) Zlib enabled. Server Time: 2019-06-24 14:18:17 UTC