egress illumination #154219 10/01/04 08:52 PM
Joined: Jul 2004
Posts: 19
J
jsherrard Offline OP
Member
I need help with comments that a plan reviewer made about egress illumination in a commerial office building. He refered to the North Carolina Fire Prevention Code 1003.2.11 that says "The means of egress, including the exit discharge, shall be illuminated at all times the building space served by the means of egress is occupied." His comments indicate to satisfy this requirement there has to be either a wall switch and light at the egress or night-lighting. This is inside the building, not outside and is not related to the requirements for normal power, not emergency lighting. I have not had this requirement noted on plans before. Is anyone familiar with this interpetation? Are there other ways to satisfy this requirement?

Building Codes & Related References
Re: egress illumination #154220 10/02/04 05:34 PM
Joined: Aug 2003
Posts: 1,374
R
Ryan_J Offline
Moderator
I'm not familiar with NC rules and regulations, but the reviewer is correct regarding the emergancy illumination. All portions of the means of egress that are large enough to require two exits (including outside at the exit discharge) are required to have emergancy illumination. I find the comments a little strange, but the way I always see this requirement satisfied is by placing emergancy lighting at the outside of the exit doors, and all other areas requiring the illumination.


Ryan Jackson,
Salt Lake City
Re: egress illumination #154221 10/28/04 08:08 PM
Joined: Dec 2003
Posts: 751
E
earlydean Offline
Member
The exit discharge is the area outside the building, giving the fleeing occupants access all the way to a public way (street, parking lot or alley). In these larger buildings, this "night-light" is required to be lit at all times during darkness when the building is occupied, just the same as the EXIT lights and other egress lighting (night-lights or emergency lights) throughout the building.
A switched porch light would not qualify as this required egress lighting. A photo-cell or time-clock controlled porch light might fit the bill.
All egress and EXIT lighting needs to be on an emergency circuit, or have battery back-up power.


Earl

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,022 Are you busy
205,034 Re: Forum
193,139 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3