hanging from bottom cord of truss. #154088 03/11/04 11:12 PM
Joined: Mar 2001
Posts: 345
T
tdhorne Offline OP
Member
We were building a pharmaceutical laboratory into the shell of a tilt up warehouse. We built trapeze racks to carry the conduit but we hung the rod off of the bottom cord of the trusses. The AHJ declined concealment until we transferred the load to the top cord of the trusses. I don't doubt that some code requires this but with the largest conduit being one inch and the trapeze being one foot wide I thought it a bit petty.
--
Tom H


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Building Codes & Related References
Re: hanging from bottom cord of truss. #154089 03/11/04 11:40 PM
Joined: May 2001
Posts: 717
G
George Corron Offline
Member
A bit petty indeed. I'd fire off an RFI (Request for information) to the structural engineer. This is a new one for me. The SE may tell you the same, but I do believe they are intended to carry supplemental structure, but can not see your plans or load data from here.

May be as simple as a phone call, but could save you a lot of time and money.

Re: hanging from bottom cord of truss. #154090 03/12/04 01:13 AM
Joined: Aug 2001
Posts: 599
N
Nick Offline
Member
Petty with that size rack for sure. I have run into this a number of times. Usually they will let you hang from the bottom if you make your attachments at the panel point.

Re: hanging from bottom cord of truss. #154091 03/12/04 10:16 AM
Joined: Aug 2003
Posts: 1,374
R
Ryan_J Offline
Moderator
I can see both sides of this issue. I agree that the weight we are talking about is rather light, but I can understand the inspector's concern. I personally would not have said anything about it if I were inspecting it.

The problem that I have is that your inspector is requiring you to go off of the top chord...did he review the truss engineering and perform the calculations to verify that the top chord could carry the extra weight? [Linked Image]

I agree with George...send the PE an RFI and he'll giggle for a minute and tell you everything is OK.


Ryan Jackson,
Salt Lake City
Re: hanging from bottom cord of truss. #154092 03/16/04 10:50 AM
Joined: Dec 2003
Posts: 751
E
earlydean Offline
Member
The BO is only trying to do his job. If he doesn't have the experience or knowledge to determine that the extra weight of your trapeze can be handled by the bottom chord, then he should have asked you to get your permission slip from the engineer or remove the rack. We teach that trusses are designed to carry the weight on the top truss. This BO apparently took that as meaning all weight, no matter how light, would have to be from the top. In time, this BO will understand that small weights can be supported from the bottom. Until then, get the engineer to write you up an OK.


Earl
Re: hanging from bottom cord of truss. #154093 03/16/04 05:19 PM
Joined: Dec 2003
Posts: 35
S
swedejr Offline
Member
We generally hang off the bottom of the truss also; But most fitters will hang off the top of the truss. I've never found out the actual reason, but I'd have to assume it's the stress loading on the truss....

Re: hanging from bottom cord of truss. #154094 03/16/04 05:35 PM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
You guys are spoiled [Linked Image]

99% of the jobs we are on we can not hang a 4" square off the bottom chord of a truss or I-Beam.

It is almost always in the specifications that no loads are to be placed on the bottom chord or web.

If it is an I beam structure this means using threaded rod up to the top web for even small single raceways on minnis.

It has always seemed a little extreme but it keeps it easy to enforce, no fussing around with figuring out what is to much and what is OK.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,742 Are you busy
204,967 Re: Forum
193,085 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3