#154083 03/10/04 08:24 PM
Joined: Aug 2001
Posts: 599
N
Nick Offline OP
Member
This sort of goes with the question below but a different application. In a hospital setting the plans show three power panels surface mount in an exit corridor. Besides being a bad location I am looking for code references prohibiting it. (UBC, CEC ADA etc.) Does anyone now off hand?

Horizontal Ad
#154084 03/10/04 10:16 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
The only thing that I can think of would be that if the panel is deeper than 4", and is set higher than 27" it is a no-go.


Ryan Jackson,
Salt Lake City
#154085 03/10/04 10:20 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
Nick: I just noticed that you are in California and therefore under the Uniform code. I think this provision still applies to your code, but I'm not 100% sure.


Ryan Jackson,
Salt Lake City
#154086 03/11/04 08:07 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
Hi Nick. Please understand that my knowledge of the 97 UBC is pretty limitted, much less the California Building Code. From what I have read, the 4" projection rule doesn't apply to the UBC. With that in mind, barring a local amendment, I can see no violation in placing your panel in the hallway.


Ryan Jackson,
Salt Lake City
#154087 03/11/04 09:37 PM
Joined: Aug 2001
Posts: 599
N
Nick Offline OP
Member
Thanks for the info. [Linked Image] I wanted to quote a code violation but instead I just brought it up to the GC today. I'll still have to write the RFI so I can steer them in the right direction to move them to. As it turns out this corridor will be a major though fare for the staff. There is bumper gard going at +42" so they will have to move merely based on that.


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Theelectrikid
Theelectrikid
Levittown, PA
Posts: 812
Joined: April 2004
Top Posters(30 Days)
Popular Topics(Views)
333,537 Are you busy
258,891 Re: Forum
240,318 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5