#154066 02/22/04 11:05 PM
Joined: Feb 2004
Posts: 41
R
rknikko Offline OP
Member
Can I move the existing panels from the basement to the ground level public hallway in a 2 family house. I'm doing this because I am moving the existing meters from the basement to the outside of the house? Normally, the panel will be in the tenant's unit, but in this case I am not sure whether it can be installed in the hallway or not. Please help. Thank you.

Building Codes & Related References
Joined: Aug 2003
Posts: 1,374
R
Moderator
I don't see any reason why not. You should be fine. [Linked Image]


Ryan Jackson,
Salt Lake City
Joined: Sep 2001
Posts: 25
D
Member
You may want to check and make shure that this is not a 1 hour rated wall. If it is, you will not be able to mount this panel in the wall. If it isn't rated, then I don't see a problem.

Joined: Feb 2004
Posts: 41
R
rknikko Offline OP
Member
What is a 1 hour rated wall? How can I tell?

Joined: Dec 2003
Posts: 751
E
Member
You can tell because the sheetrock (Gypsum wallboard) will be type X, and usually two layers. Type X has a different shade to it, somewhat darker than non fire rated sheetrock. In a two family, so long as you stay away from the wall that separates the two apartments, you should be OK. If it is, you can still manage by boxing your panels in with a rated partition. Remember to seal all penetrations with rated fire/draft caulk.

Earl


Earl
Joined: May 2002
Posts: 1,716
R
Member
Don't take this the wrong way, but are you permitting this work?

Being that this is a "public" building or atleast not just your residence, you should have this work performed by a licensed electrical contractor.

You did not list your occupation in your profile.

Roger

Joined: Dec 2000
Posts: 4,287
Member
Look at the plans to find rated walls.
Not just at the "E" sheets.
Try the "A" sheets. Very often I've found discrepancies between the "E" and "A" sheets.
BTW, in court, it will be the "A" sheets (reflected ceiling plan) that take precedence...S

[This message has been edited by electure (edited 02-29-2004).]


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Top Posters(30 Days)
Admin 13
Trumpy 10
Popular Topics(Views)
280,356 Are you busy
213,431 Re: Forum
200,352 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5