#154059 02/20/04 11:02 PM
Joined: Oct 2003
Posts: 259
J
Joey D Offline OP
Member
I am on a job in a apartment building where the floors are all concrete. The contractor is framming a few areas in he middle of the ceiling to install recesed lights in. He has cut a 2inch deep trench in the ceiling from one lowered ceiling to the new one. The floors are only 8" deep. Would this be a smart thing to do?

Stay up to Code with the Latest NEC:


2020 NEC & Related Reference & Study Guides
2020 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with these Exam Prep Combos:
 

>> Master Electrician Exam Prep     >> JourneyMan Electrician Exam Prep
 

Joined: Oct 2003
Posts: 147
C
Member
The only person who could answer that question is the Engineer who designed the building. If the engineer gave the contractor the go-ahead for this trench and the corresponding repair, then it should be okay.

Joined: Jan 2003
Posts: 4,391
I
Moderator
I agree with Crash.

Any chance these are precast cement decks?

If yes as long as the pre-stressed cables inside are not cut it seems you can do a lot to them, with an engineers OK.

Without an engineers OK this sounds dangerous.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: May 2002
Posts: 1,716
R
Member
I agree with Crash and Iwire. A structural engineer would need to be involved, and it would seem to me that there would be some specific instructions to the cutting.

Roger

Joined: Jun 2003
Posts: 1,143
D
Member
I was going to ask if they were Spancrete, or another type of cellular concrete. Taking 2" out of that could be, uh, problematic.

Get a Structural Engineer's opinion.

Joined: Sep 2003
Posts: 200
U
Member
I work in mainly new highrise construction. Typical floors are 190mm (approx 7-1/2") and having to chip a shallow trench in the ceiling or floor (to bury BX cable or 1/2" ENT) has not been an issue with the engineers or inspectors so long as the steel isn't cut. Usually we don't have to go deeper than 1" or so, unless there's a spot where the rebar is too shallow and we have to go behind it.

Check with YOUR engineer first though [Linked Image]

[This message has been edited by u2slow (edited 02-21-2004).]

Joined: Oct 2003
Posts: 259
J
Joey D Offline OP
Member
Thanks. I was thinking the same.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician