Generator #154026 01/29/04 06:01 PM
Joined: May 2002
Posts: 5
Z
Zapper Offline OP
Junior Member
My firehouse wants to put a 5kw generator in the truck bay area for use on the garage doors only. I told them NG. You can,t put a generator inside the bay. Must have a special room for the unit. Plumber want's to connect it to the gas line inside and vent out-NG,NG! Where will I find the codes for this applaction needed to do this job correctly? Building codes & NEC codes

Building Codes & Related References
Re: Generator #154027 01/29/04 06:20 PM
Joined: Aug 2003
Posts: 1,374
R
Ryan_J Offline
Moderator
2002 NEC 445.10?


Ryan Jackson,
Salt Lake City
Re: Generator #154028 01/29/04 09:48 PM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
If he can vent out the combustion exhaust, I don't know of a code violation.
The trick is venting out the exhaust. No 5kW unit that I have ever seen is capable of having its exhaust piped remotely. You could basterdize the exhaust, then Ryan's code section would apply.
The process is similar to having a gas fireplace in the building, if it is piped out properly, then flame away.


Ron
Re: Generator #154029 01/29/04 11:58 PM
Joined: May 2001
Posts: 717
G
George Corron Offline
Member
You need NFPA 110, and (I think) 54 Fuel gas code. There is nothing preventing running the exhaust outside and placing genset inside, it's done all the time, usually with schedule 40 or 80 black pipe.

The fire truck engines run inside, so can the genset, but just like you put the exhaust tubes on the trucks to work on them, be careful with the exhaust. You do need a drain at the low point, and must consider any windows, etc.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 20
Popular Topics(Views)
272,228 Are you busy
206,116 Re: Forum
194,105 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3