#152761 12/22/05 12:24 AM
Joined: Oct 2000
Posts: 3,672
Likes: 4
Admin Offline OP
Administrator
Member
Quote
We will be re-habing this next month. Appears to be in fair condition. Anything specific we need to look for? (i.e. replacing push-o-matic breakers, re-tourquing etc.)

- LearJet9
[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]

Horizontal Ad
#152762 12/22/05 09:51 AM
Joined: Jun 2003
Posts: 681
P
Member
On a quick look, the grounded conductors and the Equipment grounding conductors are on the same bus...is this the service disconnect, or downstream of it?


Pierre Belarge
#152763 12/23/05 12:46 AM
Joined: Feb 2005
Posts: 693
L
Member
This could be service equipment if you can deenergize the entire service with six throws of a 2 x 12.


Larry Fine
Fine Electric Co.
fineelectricco.com
#152764 12/27/05 09:15 AM
Joined: Apr 2005
Posts: 197
L
Member
Immediatly to the left of what you can see in the main disconnect, 800A I beleive. We will be replacing about 100 push-o-matic devices and checking all connections for tightness. We will of course address any other issues we find while in there. The guys working on this job have never seen bull-dog equip before.

#152765 12/27/05 09:47 AM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
How many pole positions are in the common backbox, >42?
Will you replace the guts with a new panelboard with individual backboxes. I was in a jurisdiction that would allow the reuse of a old backbox for new panelboard guts (not UL listed together).


Ron
#152766 12/27/05 03:33 PM
Joined: Apr 2005
Posts: 197
L
Member
Each seperate section has 40 positions in 2 banks. Each section is controlled by 2 contactors, 1 for each bank of 20 devices. As far as I know at this time, we will only be replacing individual devices, and then only about 80 out of 120. (?) We will be checking all terminations to make sure they are secure. Panel schedules are all incorrect but they declined to have us do a new panel schedule.

#152767 12/28/05 12:39 AM
Joined: Sep 2002
Posts: 946
Likes: 3
N
Member
In pic #3, are you going to replace the GE and FPE breakers?

P.S. The subject of mixing different manufactures breakers in the same enclosure would be a good thread all by it self.

Horizontal Ad
#152768 12/28/05 05:32 AM
Joined: Jul 2002
Posts: 8,441
Likes: 4
Member
Just a little question,
How did it get the name Bull-Dog?. [Linked Image]

#152769 12/28/05 08:19 AM
Joined: Dec 2000
Posts: 4,293
Member
You need to get rid of that aluminum ladder before someone gets hurt.

#152770 12/28/05 11:26 AM
Joined: Sep 2002
Posts: 946
Likes: 3
N
Member
Bulldog electric,it was a I-T-E subsiduary, now part of Siemens.


BTW, its "Pushmatic" [Linked Image] [Linked Image]

Page 1 of 2 1 2

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Top Posters(30 Days)
Admin 3
CSS 1
Popular Topics(Views)
366,499 Are you busy
289,476 Re: Forum
268,104 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5