Joined: Jun 2004
Posts: 202
3
32VAC Offline OP
Member
March 22, 2007 08:51am
Article from: AAP

A MAN has been electrocuted on his north Queensland property overnight.

Police say the 64-year-old man died after walking on a fallen powerline in long grass at Mission Beach around 7.20pm (AEST).

He had been checking out his property with his 30-year-old son after losing power.

The son suffered a minor shock when he tried to help his father who died at the scene.

Police said two powerlines had been brought down, possibly when a bird flew into them.

Investigations are continuing but police said there were no suspicious circumstances.

http://www.news.com.au/story/0,23599,21426281-1702,00.html

Arc Flash PPE Clothing, LOTO & Insulated Tools
Joined: Jul 2002
Posts: 8,432
Likes: 3
Member
Thanks for that report 32VAC.
My advice to anyone out in the more rural areas, if you lose power, stay indoors.
You can do nothing until a person trained in HV equipment gets to your place.
Going to find a downed power line is one of the silliest ideas this side of the black stump.
The further you are out from a city, the higher the voltage will be too.
I don't think that this guy actually stepped on the downed line, I think that he got so close to it that the step voltage over-rode the insulation value of his footwear.
With some of the more rural areas using voltages in the 10's if not 100's of kV's this is a real worry.
Think of a situation like this as the same as dropping a stone into a pool of water.
The stone is where the cable fell, now you are depending upon a recloser or it could even be an SWER line, where the point of origin of the circuit could be miles away.
High resistance joints (over time) could compromise the protection system, these things are hardly ever tested in rural areas
mean that the chances of a fault clearing could take a lot longer than usual.
Back to the pool of water, if you happen to tread between the ripples, you have a potential difference on each foot, the closer you get to the stone, the higher the step potential difference.
Peoples shoes have melted in some cases, where 11kV lines have fallen here.

Joined: Jan 2006
Posts: 558
R
Member
Then again you have people that are pure idiots and have tried to MOVE a downed power line. Yes, its the truth, it happened a block from here!

A.D


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,158
Joined: May 2003
Top Posters(30 Days)
BigB 3
triple 2
Popular Topics(Views)
305,040 Are you busy
233,458 Re: Forum
218,145 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5