W
Member
Was told by the Authority Having Jurisdiction today that GFCI's were required in a manufacturing facilities lunch room within 6 feet of sink. I thought this was a dwelling only rule. Have I been wrong all this time? When I asked for the article I was reffered to 90-4.

Horizontal Ad
Joined: Aug 2001
Posts: 599
N
Member
You are correct. See 210-8(b. Just another case of an inspector enforcing his rules and falling back on 90-4. How he can "interpret" a lunch room sink as having anything to do with
(1)bathrooms , or
(2)rooftops
is beyond me.

Joined: Oct 2000
Posts: 2,749
Member
210.8(B)(3) in the 2002 NEC requires all 15- and 20-ampere, 125-volt receptacles in nondwelling-type kitchens to be GFCI protected.

We are still faced with the question:

"What is a kitchen?"

Did the AHJ clarify this for you, and are you using the new 2002 code?


Joe Tedesco, NEC Consultant
Joined: Oct 2001
Posts: 172
W
Member
Sorry for not originally posting in the NEC area. This county is still under the 1999 code until January 1 2003. After borrowing my GFCI tester to check the outlets, I mentioned to him that the receptacles in question did not require GFCI protection. My statement was met with a GFCI's are required by code anywhere within 6 feet of a sink. When I inquired as to the article he was reffering to He said 90-4. At which time I said oh yea now I remember that the word dwelling does'nt preceed the requirements for GFCI's at sinks. I could tell that I was not going to win the battle, so I stuck to my long held position of refusing to be drawn into a battle of wits with an unarmed man. Also the better part of valor or common sense wouldn't let me rub his nose in it, as he is still the AHJ. He passed the job without requiring the GFCI's, but the sad part is he still thinks they are a NEC requirement in this location.

Joined: Jan 2002
Posts: 1,457
E
Member
If he thinks they are a requirement and he passed you without requiring them I would have to say he is not much of an inspector. 1999 NEC 210-8 (b) Other than dwelling units. Bathrooms and rooftops. Is the lunch room in either of these locations? 90-4 DOES NOT give permision to the AHJ to change the code as written, the allowance is for intrpretation. There is a big difference between those two. 2002 Does require them in kitchens but as has been stated when does a lunchroom become a kitchen. I would argue there must be a range or stove of some type. Not portable appliances like a toaster oven or microwave as these could be used in any room.

Joined: Jul 2002
Posts: 241
S
SJT Offline
Member
As far as I know, any 110v receptacle located within 6' of any sink, no matter where it's location in any room may be, has to be GFCI protected. If there is a sink you have to think GFCI. After all, it's a safety thing and there should'nt be any doubt about the GFCI.
Have a nice day

Joined: Oct 2001
Posts: 172
W
Member
SJT are you an inspector too? I agree that safety and best design would provide the GFCI protection, but where do you and the AHJ read in the 1999 NEC that they are required. I have studied the code in an attempt to make code compliant installations, and I have missed the particular article that is being referenced.
What is the number?????????????????

Horizontal Ad
Joined: Jul 2002
Posts: 241
S
SJT Offline
Member
I'm sure it's not a big job to put the GFCI in.
I understand the confusion here, but the AHJ does call the shot. I my self am not an inspector but am licensed and certified with 2 out of 3 exams from the IAEI. I hope to take the exam on 1 and 2 family dwellings soon. It will certify me as an inspector, but I'll be doing it for my own satisfaction and concern for the trade.
Have a great day

Joined: Nov 2000
Posts: 2,236
Likes: 1
Member
Was the "6' GFCI rule" in the code at one time?

That would be my guess, maybe in the '90 or '93?

That's about the timeperiod I had learned that rule, but I wasn't too serious about code then, either.

I'm wondering if it's another one of those "assumed rules" or if it actually existed at one time, to be replaced with the verbage that requires GFCI for the entire countertop and room (residential kitchens and baths).

Anyone know?

[This message has been edited by sparky66wv (edited 10-03-2002).]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Joined: Jan 2002
Posts: 1,457
E
Member
I recall that it was within six feet of a sink the kitchen but that's about it. SJT I take great exception to you saying that the AHJ calls the shots. You and I would certainly not get along on the job. It is the NEC that calls the shots where I work.

Page 1 of 2 1 2

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Admin
Admin
NY, USA
Posts: 3,685
Joined: October 2000
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
331,557 Are you busy
256,778 Re: Forum
238,620 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5