SE Cable Length #14768 10/01/02 07:41 PM
Joined: Jan 2002
Posts: 13
R
Ron Hoback Offline OP
Member
I was just wondering what the permissable length of SEC into a residence before it reaches the service dissconnect that is allowed in your areas. Our area is six foot.

RonH

Work Gear for Electricians and the Trades
Re: SE Cable Length #14769 10/01/02 07:59 PM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
10' here in Vt.

Re: SE Cable Length #14770 10/01/02 08:29 PM
Joined: Nov 2001
Posts: 280
M
motor-T Offline
Member
In Ohi-yo its land it as soon as practicable.
Mark

Re: SE Cable Length #14771 10/01/02 09:05 PM
Joined: Apr 2002
Posts: 7,177
HotLine1 Offline
Member
Here in our area of NJ it goes like this:
Land it ASAP; keep it as "short" as possible; not to exceed xx feet; "at the discression of the AHJ", and a few other ones.

"A reasonable distance"???

Boy, I'm glad we don't do houses.

John


John
Re: SE Cable Length #14772 10/01/02 09:36 PM
Joined: Jan 2002
Posts: 324
A
arseegee Offline
Member
Gotta be back to back here. No exception!

Re: SE Cable Length #14773 10/01/02 10:54 PM
Joined: Nov 2000
Posts: 2,236
sparky66wv Offline
Member
Here, in Allegheny Power Country, we have to provide a disconnect anytime the meterbase and Load Center are not "back to back"...

However... "back to back" has become loosely translated to mean back to back, or side by side, or in the same stud bay, or in the same general area...

I've seen as much as 10' vertical distance from the Meterbase and Load Center and was considered OK...

Seems to be a gray area...


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: SE Cable Length #14774 10/01/02 11:21 PM
Joined: Sep 2002
Posts: 111
S
Sean WB Offline
Member
Back to Back if possible, AHJ decides if it was possible. so I just put the darn disconnect outside [Linked Image]
I am going to do a 200A service upgrade tomorrow.... you guys have to see the current service. I'll take a pic for you


I did not get as think so badly as you shocked I did.

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 8
Popular Topics(Views)
266,149 Are you busy
200,995 Re: Forum
189,679 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3