Accidents Caused by Ground Faults #146887
02/09/01 03:21 PM
02/09/01 03:21 PM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Ground Faults that caused accidents:
http://www.osha.gov


[This message has been edited by Joe Tedesco (edited 03-21-2001).]


Joe Tedesco, NEC Consultant
Arc Flash PPE Clothing, LOTO & Insulated Tools
Re: Accidents Caused by Ground Faults #146888
02/11/01 01:05 PM
02/11/01 01:05 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,372
A lot of cord connected scenario's here, note # 126052380...the one where the water dept. gets a tickle undooing the underground h2o line...
[Linked Image]

This could happen under a code compliant situation

Re: Accidents Caused by Ground Faults #146889
04/19/01 08:07 PM
04/19/01 08:07 PM
A
Anonymous
Unregistered

http://www.osha.gov/cgi-bin/inv/inv1xp?s=170165856027 :
"A temporary power pole equipped with a ground-fault circuit interrupter supplied the trailer, and this was found to be wired correctly by city building inspectors. (the original report did not state why the ground-fault interrupter did not trip.)"

But it was probably because it was wired wrong!

Re: Accidents Caused by Ground Faults #146890
04/24/01 09:06 PM
04/24/01 09:06 PM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,905
NY, USA
Dspark,

There has been a sort of survey conducted recently that reports a very large percentage of non-working GFCIs are in the field. It is suggested that many are damaged by exposure to weather and power surges. This may be one that falls into that category.

I once came across a pool light (120v) with a broken lens (water in the fixture) that did not trip a properly wired GFCI receptacle. The GFCI cover was damaged or missing and I think that the contacts must've been rusted in place.

Bill

Re: Accidents Caused by Ground Faults #146891
04/24/01 10:39 PM
04/24/01 10:39 PM
A
Anonymous
Unregistered

Quote
There has been a sort of survey conducted recently that reports a very large percentage of non-working GFCIs are in the field. It is suggested that many are damaged by exposure to weather and power surges.

I have yet to see a non-working GFCI for any reason other than reversed line and load.

But that is because there are so few of them anyway.

I know that even I don't test my GFCIs monthly. In fact I just recently got my sons to test them all upstairs. I think I have one in the basement that hasn't been tested for a year and a half.

Quote
This may be one that falls into that category.

Perhaps so. Silly me, when I read that report I thought it said that it was wired incorrectly.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,538 Are you busy
190,772 Re: Forum
180,494 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 14 (0.006s) Memory: 0.9665 MB (Peak: 1.1069 MB) Zlib enabled. Server Time: 2019-04-23 08:22:38 UTC