Ground Faults that caused accidents:
http://www.osha.gov


[This message has been edited by Joe Tedesco (edited 03-21-2001).]


Joe Tedesco, NEC Consultant
Horizontal Ad
Joined: Oct 2000
Posts: 5,393
S
Member
A lot of cord connected scenario's here, note # 126052380...the one where the water dept. gets a tickle undooing the underground h2o line...
[Linked Image]

This could happen under a code compliant situation

A
Anonymous
Unregistered
http://www.osha.gov/cgi-bin/inv/inv1xp?s=170165856027 :
"A temporary power pole equipped with a ground-fault circuit interrupter supplied the trailer, and this was found to be wired correctly by city building inspectors. (the original report did not state why the ground-fault interrupter did not trip.)"

But it was probably because it was wired wrong!

Joined: Oct 2000
Posts: 4,140
Likes: 4
Member
Dspark,

There has been a sort of survey conducted recently that reports a very large percentage of non-working GFCIs are in the field. It is suggested that many are damaged by exposure to weather and power surges. This may be one that falls into that category.

I once came across a pool light (120v) with a broken lens (water in the fixture) that did not trip a properly wired GFCI receptacle. The GFCI cover was damaged or missing and I think that the contacts must've been rusted in place.

Bill


Bill
A
Anonymous
Unregistered
Quote
There has been a sort of survey conducted recently that reports a very large percentage of non-working GFCIs are in the field. It is suggested that many are damaged by exposure to weather and power surges.
I have yet to see a non-working GFCI for any reason other than reversed line and load.

But that is because there are so few of them anyway.

I know that even I don't test my GFCIs monthly. In fact I just recently got my sons to test them all upstairs. I think I have one in the basement that hasn't been tested for a year and a half.

Quote
This may be one that falls into that category.
Perhaps so. Silly me, when I read that report I thought it said that it was wired incorrectly.


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,443
Joined: July 2002
Top Posters(30 Days)
BigB 6
Popular Topics(Views)
329,661 Are you busy
254,498 Re: Forum
237,002 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5