the service is as such: residential 200A overhead, seu drop to meter pan, pvc nip to nema 3r breaker enc, 4 cond seu to main lug panel in house. there is a well with plastic piping into house, and since this is my first install where city water piping doesn't exist i'm not sure how to ground the system. I drove 2 g/r w/ the usual #6 but i'm don't think that is enough. Please shed some insite
|
|
|
|
Joined: May 2001
Posts: 717
Member
|
You're done!! You must bond the water pipe to the service. If you like, you can catch the water pipe on the way to the ground rods, or run a separate conductor out of the service to catch it.
Suggest - bond around fiberglass collar on ductwork at unit.
|
|
|
|
Joined: Jul 2002
Posts: 38
Member
|
Here in Oregon, if this was new construction, a ufer ground would also be required.
|
|
|
|
Joined: Jan 2002
Posts: 324
Member
|
Might want to check your GEC w/ 250.66. Think you'll need a #4 copper for the 200A service.
[This message has been edited by arseegee (edited 09-28-2002).]
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
arseegee, As long as the GEC is only going to a rod, #6 is the largest that the code requires. See 250.66(A). Don
Don(resqcapt19)
|
|
|
|
Joined: Jan 2002
Posts: 324
Member
|
Don, has this changed for 2002, I was taught that if a driven rod is your only GE then you size the GEC from the table. I thought you only used #6 if the rod was a supplemental electrode... guess I'm confused.
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
arseegee, No change in the code rule, however in the '96 and earlier codes this rule was Exception #1(a) to 250-94. The rod really isn't a very good electrode and it will never carry very much current into the earth. A #6 is more than enough copper to carry the current that the rod can put into the earth and that is why the rule exists. There is no electrical advantage to installing a larger GEC to the rod. Don
[This message has been edited by resqcapt19 (edited 09-28-2002).]
Don(resqcapt19)
|
|
|
|
Joined: Sep 2002
Posts: 37
OP
Member
|
thanks for the replys, i had all the same thoughts but wasn't sure which way to go. i wish i had gotten a rod under the basement floor
|
|
|