I recently was asked to relocate a deck box for an in the ground pool. To do this I needed to bend the brass pipe down and extend it with another stick of brass and install it into a deck box.
Problem is when I bent the pipe I created a flood. I told the homeowner that he needed to reduce the level of the water and have the light fixed. I thought it was leaking. When I spoke to the pool installer he told me that the light was supposed to leak, that is what keeps the lamp cool.
Question is: Am I being hosed? Is this true? This is a 120volt light in the pool. Something doesn’t add up. 120volt and water.. Am I whacked or what???

Horizontal Ad
Joined: Oct 2000
Posts: 4,149
Likes: 4
Member
TS,

He's right. It's a wet-niche which means that the Fixture housing is in water. It is a sealed fixture. There is water inside the conduit up to a point even with the water level of the pool. This is why the Deck box must be up higher than the maximum water level or else the box would have water in it.

Bill


Bill
Joined: Oct 2000
Posts: 5,393
S
Member
ok,
what if there were no JB, and the pipework simply went into the poolhouse?

i would imagine the same philosiphy still applys, having any splice and/or termination above H2O level???

Joined: Nov 2000
Posts: 2,148
R
Member
Sparky,
680.23 and .24 require the J-box and that it have the bottom at least 8" above the highest possible water level.
Don


Don(resqcapt19)
Joined: Oct 2000
Posts: 5,393
S
Member
I am missing it Don, i see where a JB is talked about, but not specifically required.

I suppose that i could put one in the pool house where the pool fixture runs both go?

bail me out please.......
[Linked Image]

Joined: Jun 2001
Posts: 642
N
Member
Wet niche light fixtures come with a cord attached. You have to install the j-box close enough to allow the light fixture to be removed from the niche, set up on the pool deck (while unwinding the cord) then open up the fixture to replace the bulb. The cord usally will not reach to a pool house. This is why the pool junction box is located as close as 4 feet from the pool edge and is to be 8" above the max water level.
This allows you to change out the bulbs without draining the pool.
The only service call I know of where you get paid to go swimming.


ed
Joined: Apr 2002
Posts: 558
C
Member
You can get different length cords on Wet-Niche fixtures. The project I am working on now the junction boxes are about 100' from the lights.


Curt Swartz
Horizontal Ad
Joined: Oct 2000
Posts: 5,393
S
Member
whoooo boy..... [Linked Image]

live & learn.....

Joined: Mar 2001
Posts: 85
C
Member
You have to be careful with these lights too. We've had instances of the chlorine eating away the mounting hardware and the light floating to the top of the pool. This can cause the light to explode when parts of it are no longer surrounded by water. They're sometimes a fun way to break up your day if you get to go into the pool.


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 264
Joined: February 2013
Top Posters(30 Days)
dsk 1
Popular Topics(Views)
338,285 Are you busy
263,701 Re: Forum
244,031 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5