#14363 09/19/02 06:20 PM
Joined: Jul 2001
Posts: 311
F
Member
If a circuit breaker is used as an overcurrent protective device for air conditioning equipment must it be marked "HVAC"?
I've searched Article 240 and could not locate that as a requirement.
I found SWD and HID marked circuit breakers (NEC 240.83(D) but no requirement for HVAC.

Horizontal Ad
Joined: Apr 2002
Posts: 7,411
Likes: 7
Member
Frank:
I can't give articles as my NEC is at the office.
The nameplate that is on the condenser unit, states either FUSE or HACR CB as the required overcurrent protection required for each unit.
We have to follow the mfg instructions, and use the nameplate data.
IF it says "fuses" then the circuit must be protected by fuses. If it says "HACR CB" then a HCAR CB in the panel and a non-fused disco at the unit.
Somebody post the articles please.

The above is stated IMHO, as "Sparky66WV says
John


John

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43
Joined: September 2013
Top Posters(30 Days)
Popular Topics(Views)
347,128 Are you busy
272,234 Re: Forum
252,600 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5