ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
How's Florida doing with Hurricane Ian?
by Bill Addiss - 09/28/22 12:41 PM
Tough being a lineman's kid
by Bill Addiss - 09/28/22 12:39 PM
GFCI's pops in large numbers
by dsk - 09/26/22 04:35 AM
AFCI’s Revisited
by sparky - 09/24/22 09:58 AM
NFPA Price Increase Coming
by Bill Addiss - 09/23/22 02:22 PM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
0 members (), 15 guests, and 13 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#14229 09/17/02 12:10 AM
Joined: Sep 2002
Posts: 3
U
Junior Member
Do we have to bond the insulated grounding wire of MC cable to a metal box? Isn't the metal jacket enough? If so, what do you do in the case of an Isolated grounding receptacle? Mike

#14230 09/17/02 06:55 AM
Joined: Mar 2001
Posts: 2,056
R
Member
The jacket of standard sriral wound MC cable is not sufficient to provide grounding without supplemental grounding conductors.
See 250.118(11).
As far as your installation, there is an assortment of special MC cables available. This includes those that have additional grounding conductors.

BTW,
If you have a handbook, the commentary following 330.108 explains this situation.

[This message has been edited by Redsy (edited 09-17-2002).]

#14231 09/17/02 07:05 AM
Joined: Sep 2002
Posts: 5
L
Junior Member
The NEC does not allow the device (receptacle) to bond the box. Since the MC sheath is not rated for grounding, you must ground the green wire to the box. Here we use a green wire pigtail that comes with a #10 screw available a most any supply house. This screws to the tapped ground screw hole in the box. We use a special green wirenut with a hole in it that allows the green wire to be stripped out bare long enough to reach the receptacle after it leaves the wirenut.

#14232 09/17/02 07:09 AM
Joined: Sep 2002
Posts: 5
L
Junior Member
As for as using MC for IG installations, you can order MC cable with both a solid green conductor and a green/yellow stripe conductor. It's not really cost effective to use that cable. You might as well use conduit. MC comes in about any configuration you want. I believe you can get it in large feeder sizes as well. I am bidding a job that calls for weatherproof (pvc jacketed) #8 MC to run on the bottom of sewage treatment ponds to aereator motors!


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 240
Joined: March 2005
Top Posters(30 Days)
dsk 3
Popular Topics(Views)
297,765 Are you busy
228,511 Re: Forum
213,342 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5