#139956 01/06/04 07:39 PM
Joined: Jun 2002
Posts: 159
L
Member
On attempting to measure the earth electrode resistance on a single-phase TT installation using an AVO earth loop impedance tester, the instrument indicated over limit voltage of 290v and would not permit the test to proceed.
The P-N voltage was 235v. Unfortunately the operative did not measure neutral to earth voltage.
A contractor on site at the same time as our operative confirmed the 290v using a different voltage indicator.
I was intrigued and some days later I visited the site. Voltages seem to have returned to normal, 233v between live conductors and between phase and earth and 0 v between neutral and earth.
The supply to the installation is fed via a local three phase power company tx.

Care to speculate?


regards

lyle dunn
Joined: Aug 2001
Posts: 7,520
P
Member
Maybe a bad neutral somewhere on the network?

Joined: Jan 2004
Posts: 105
C
Member
Imbalance on delta tx?

Joined: Jul 2002
Posts: 8,407
Member
lyle,
Would you care to give the type of Line-Earth loop tester used? (ie: Model No.)

Joined: Jun 2002
Posts: 159
L
Member
Trumpy,
Sorry Trumpy, misinformation! The instrument was actually a Robin loop tester. It appears that the indicated voltage can be out by 10% although this wouldnt have necessarily been the problem.
The installation was not connected to the supply at the time. The NIE engineer suggested capacitance which disappeared when the installation was connected. Not sure about that one!
Many thanks for your replies guys!


regards

lyle dunn

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Top Posters(30 Days)
Trumpy 10
Admin 10
Popular Topics(Views)
280,437 Are you busy
213,517 Re: Forum
200,399 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5