I`ve been seeing lots of concerns over older gfci rec failing but allowing power to be used unprotected.My question is is it the same for older GFCI breakers.Also One of the ecm code questions was about the bundling of wires when you go through web beams with the 1 1/2 holes and you run several wires in them how are you guys dealing with this.Thanks in advance.
If you bundle 10 to 20 current carrying conductors, the derating factor is 50%. If you have no more than 6 outlets at 180 VA each on the circuit, you would still be OK for derating with out increasing the size of the conductors (assuming #12 wire and 20A circuit).
Reference:
310.15(B)(2)(a)
Note: EGC's and Multiwire "true" neutrals are exempt from the conductor count.
<disclaimer> This is how I interpret it. </disclaimer>
[This message has been edited by sparky66wv (edited 09-16-2002).]
-Virgil Residential/Commercial Inspector 5 Star Inspections Member IAEI
That would be true if you spread the cables out between the holes an undetermined amount, then I would agree, however, if the cables remain in the same general spacing from each other between the webs as compared to through them, then derating would apply.
Would it not?
-Virgil Residential/Commercial Inspector 5 Star Inspections Member IAEI