AFCI be aware #13471 09/05/02 11:42 AM
Joined: Sep 2002
Posts: 131
T
tsolanto Offline OP
Member
We do alot of new construction houses and we learned the hard way about a problem with AFCI breakers. Here it is: We were wiring a bedroom and since the bedroom had a door to a porch outside we decided to install a GFI outlet by the door, no problem right...
when the inspector came to do his thing he tested the GFI outlet by the back door with a GFI tester. before the GFI popped the AFCI breaker did. The AFCI breaker reacts faster than the GFI. Am I still code compliant? The inspector let it go. The moral is don't put GFI outlets on AFCI circuits.

Work Gear for Electricians and the Trades
Re: AFCI be aware #13472 09/05/02 06:29 PM
Joined: Dec 2001
Posts: 444
S
Sandro Offline
Member
Since the AFCI has GFI capabilities, could't you have just put a normal receptacle on the balcony and let the AFCI carry both duties?

Re: AFCI be aware #13473 09/05/02 06:53 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
The normal AFCI is not listed as a Class A GFCI and can't be used for that purpose. I think that C-H does have a combo AFCI/GFCI and that could be used. If it is a standard AFCI, I'm surprised that the GFCI tester is tripping it. The GFP circuit in the AFCI is set for 30 to 50 mA. The test current in the AFCI tester should be less than 10 mA.
Don


Don(resqcapt19)
Re: AFCI be aware #13474 09/05/02 07:41 PM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
inspedtors that show up with cheap testers, and little insight should not impress anyone.

Re: AFCI be aware #13475 09/05/02 07:42 PM
Joined: Jan 2002
Posts: 324
A
arseegee Offline
Member
For the record, a GFI tester will trip the GE arc faults too. We make sure to catch our GFI recepts off a non arc fault circuit.

Re: AFCI be aware #13476 09/05/02 09:12 PM
Joined: Jun 2001
Posts: 196
C
Cindy Offline
Member
several months ago i put a 15amp afci cb in place of my 20amp bathroom cb and left the gfci receptacle in the bathroom and have not had any tripping problems.
why do you consider using a gfci on an afci circuit a bad idea? it's just extra protection for the circuit isn't it?

Re: AFCI be aware #13477 09/05/02 09:22 PM
Joined: Apr 2001
Posts: 449
F
Fred Offline
Member
I posted here and on several other electrical forums 10 months ago that my Ideal GFCI receptacle tester consistantly tripped Siemens, CH and Square D AFCI circuit breakers. This is the test our county inspector uses on final inspection to see if bedroom receptacles are actually on AFCI protected branch circuits.

Re: AFCI be aware #13478 09/05/02 11:02 PM
Joined: Jun 2001
Posts: 642
N
nesparky Offline
Member
All the inspectors in my area use cheap GFCI testers to test the AFCI circuits. When I asked why they said because it will trip any AFCI breaker.
I wonder what they are really testing. I doubt they are testing the arc fault portion of the AFCI breaker. Maybe these inexpensive testers are not only 5-7 ma load to ground. Maybe the testers short to ground when the button is pressed.
I wonder if we really were accuratly testing GFI outlets and/or breakers at all.
Maybe these testers need a good look at them.


ed

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 8
NORCAL 3
Popular Topics(Views)
269,954 Are you busy
204,379 Re: Forum
192,598 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3