Fire or safety concerns about receptacle loads #13375 09/02/02 12:36 PM
Joined: Dec 2001
Posts: 270
E
Elzappr Offline OP
Member
Art 210 requires stationary equipment that takes up 50% of a circuit's capacity to be a dedicated circuit. Other than engineering or usage convenience considerations, is there a safety issue? I recently had to repair a damaged installation that apparently was modified by a maintenance person AFTER initial construction, so that it violated the 50% rule. They tapped into a large role up door opener (in a commercial building) to provide power for a couple of convenience outlets. I don't like driving customers away by re-engineering existing installations because of code issues which aren't obvious safety issues. Anyone have some perspective about what is so dangerous about violating the 50% rule?

Work Gear for Electricians and the Trades
Re: Fire or safety concerns about receptacle loads #13376 09/02/02 03:41 PM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
the fallicy is, that anyone can 'dedicate' a circuit without consultation......

Re: Fire or safety concerns about receptacle loads #13377 09/02/02 03:45 PM
Joined: Aug 2001
Posts: 7,520
P
pauluk Offline
Member
As I see it, the problem with violating such a rule would be that if/when other high-power appliances are connected to the circuit, there could be a high incidence of nuisance tripping.

That in itself wouldn't be a problem so long as the OCPD and cables are properly sized. The only real safety issue I can see is that regular nuisance trips might lead to some uninformed person deciding to uprate the breaker in order to "solve" the problem. Then it could most definitely be a safety problem.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,034 Are you busy
205,039 Re: Forum
193,154 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3