Variable Frequency Drives #130579
07/26/06 11:37 AM
07/26/06 11:37 AM
L
LarryC  Offline OP
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
What is the difference between a 6 pulse, 12 pulse, and 24 pulse VFD?

LarryC

Tools for Electricians:
Re: Variable Frequency Drives #130580
07/27/06 02:55 PM
07/27/06 02:55 PM
J
jraef  Offline
Member
Joined: Jul 2004
Posts: 101
San francisco, CA, USA
A basic drive is "6 pulse" meaning there are 6 diodes on the front end bridge rectifier used to convert the AC to DC. If you want to reduce the current harmonics imposed on the line side supply, you can have 2x6 Pulse front ends in parallel (12 pulse), one supplied by a Delta-Y transformer to create a phase shift on the AC side between the 2 rectifiers, which makes a large percentage of the current harmonics cancel each other out. If you want even further reduction of harmonics, you can do it again and have 18 pulse, even 24 pulse in extreme cases.

Jeff Raefield
Jraef Consulting www.jraef.com

[This message has been edited by jraef (edited 07-27-2006).]


JRaef
Re: Variable Frequency Drives #130581
07/28/06 07:38 AM
07/28/06 07:38 AM
W
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
jraef has described the difference between 6 and 12 (and higher) pulse rectifiers. By supplying a rectifier with higher phase counts (via suitable transformers) you can increase the number of current pulses that the rectifier draws from the supply, improving power factor.

But VSDs have both a rectifier input stage and an switching output stage, and the term 6 pulse, 12 pulse, etc can apply to the output stage.

The earliest VSD devices were termed 6 step or 6 pulse devices. They had 6 thyristor type devices arranged to connect current from the DC bus to the AC output terminals. Each thyristor would drive a single phase terminal, and could only drive that terminal positive or negative, and could only supply a single pulse of current for a third of the AC cycle. If you examined the current applied to a given motor phase, you would see that the AC cycle was approximated by six distinct steps, a very poor approximation with lots of harmonics.

Higher step devices used more complex commutation circuits to turn the switching elements on and off more rapidly than the output frequency, resulting in a greater number of steps in the output and higher fidelity synthesis of the desired output AC.

-Jon


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 7,034
Joined: April 2002
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Trumpy 3
Popular Topics(Views)
250,270 Are you busy
187,918 Re: Forum
177,451 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.004s) Memory: 0.9515 MB (Peak: 1.0770 MB) Zlib enabled. Server Time: 2018-10-16 01:58:47 UTC