240 delta CT #130328
03/09/06 09:14 PM
03/09/06 09:14 PM
D
Dnkldorf  Offline OP
Member
Joined: Dec 2004
Posts: 1,064
nowhere usa
Am I right in thinking there is 2 ways to ground the secondary of these if you do not need a nuetral.

I need a 240 transformer for a machine, due to availability I was thinking just get a 480X240 CT.

Now I just could traditionally corner ground the thing, but could I also just bond the XO and pull 4 wires. The 3 phases and EGC from the transformer?

Is one way better than the other if possible?

Dnk..

Tools for Electricians:
Re: 240 delta CT #130329
03/10/06 12:26 PM
03/10/06 12:26 PM
X
XtheEdgeX  Offline
Member
Joined: Apr 2005
Posts: 116
Florida
I've always opted to bond the XO and just pull the phases and ground.

Re: 240 delta CT #130330
03/15/06 08:02 AM
03/15/06 08:02 AM
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
Dnkldorf;

You have got it right, as far as Grounding a Closed or Open Vee Delta Secondary.

Either pick one - ONLY ONE - Line Conductor / Transformer Terminal, and make it the Grounded Conductor,

--or,

Use the Center Tap of "The Center Transformer", and bond it to Ground + Equipment, then bring out an EGC (Equipment Grounding Conductor) from the Transformer to bond the downstream equipment.

Advantage using the Center Tapped method:
Lower Voltage to Ground than with a Corner Grounding Scheme (either 120V to Ground, or 208V to Ground).
Also, if using 1 Phase 2 wire equipment, placing these loads across Lines A and C (assuming Line "B" is the "Top of the Triangle" / "Stinger Leg"), will allow the use of Circuit Breakers with Single Pole Fault Ratings at 120V (the most common breakers).

The Corner Grounded setup would need breakers with single pole fault ratings at 240V minimum - for 1 Phase and 3 Phase connected equipment / loads.
Same goes for 3 Phase loads on the Center Tap Grounded setup.

Advantage for the Corner Grounded setup:

Full sized Grounded Conductor bonded to the entire Ground Bonding scope (star point).

Good luck!

Scott35


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
cookcc
cookcc
California ,Long Beach
Posts: 28
Joined: May 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
BigB 4
Popular Topics(Views)
249,460 Are you busy
187,376 Re: Forum
176,721 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.004s) Memory: 0.9519 MB (Peak: 1.0778 MB) Zlib enabled. Server Time: 2018-09-25 20:57:41 UTC