Joined: Sep 2005
Posts: 202
W
WFO Offline OP
Member
First, I'm always getting asked by the linemen if they can bank an "X" impedance transformer with a "Y" impedance transformer. The old REA specs we have never even mention it except in the delta/delta configuration. So we (I) have always assumed that it doesn't matter in the wye/delta and wye/wye banks that we use. Is this true?

Secondly, when the REA specs DID refer to impedance balancing, they would say that the tansformers had to be within plus or minus "X" percent of each other. Were they referring to the "percent" as stamped on the nameplate, or an actual arithmetical percentage between the two (or three) values?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jan 2005
Posts: 155
D
Member
My notes state that the impedence of the transformers to be paralleled should be within 7-1/2% of each other so that they will share the load as close as possible.

Joined: Sep 2005
Posts: 202
W
WFO Offline OP
Member
Sorry, I didn't really word my question that well. I didn't mean paralleling them, just operating them together 3 phase banks.

Joined: Jan 2005
Posts: 155
D
Member
My application notes state that a D-Y bank would share equally a balanced 3ph load even though the impedance of the individual transformers may not be equal. That identical transformers should be used in D-D and open D banks. Also, Y-Y should be avoided.