CTs & shorting pins #129941
11/22/05 08:27 PM
11/22/05 08:27 PM
R
rmiell  Offline OP
Member
Joined: Nov 2000
Posts: 242
La Junta, Co. USA
I seem to have problems figuring out when shorting pins need to be in place on shorting blocks fed by CTs. One site needs pins on the unused leads, another site doesn't. reasons given for needing them is that when the current flows, it will seek a ground. If the shorting pin is not in place, it will still try to seek that ground connection, jumping over if necessary.

These are for high voltage cts, ones reading 69Kv.

Anyone have info to help me?

TIA

Rick Miell

Tools for Electricians:
Re: CTs & shorting pins #129942
11/23/05 12:50 AM
11/23/05 12:50 AM
W
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
It is my opinion that one should strongly distrust any information source which suggests that current will try to seek ground. Electric current does _not_ 'seek ground'. Instead the current follows any closed circuit back to its _source_.

In the case of current transformers, the source is the transformer winding itself. Open CT windings can develop quite high potential, enough to arc in order to close the circuit. With some of the secondary terminals properly loaded with a low impedance, it will depend upon the specific layout of the transformer to determine if any of the other terminals need to be shorted.

-Jon

Re: CTs & shorting pins #129943
11/23/05 10:19 AM
11/23/05 10:19 AM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
CTs do not like to be open circuited. It is bad (high voltage develops across the open circut) when the circuit is not carrying current, but it is extremely dangerous (arcing fault) if it is done under load.

CTs prefer a complete circuit (they have no problem with being shorted out) instead. So use the shorting pins on all leads that are not connected to a load (meter). Also use the pins before removing any existing load lead. When in doubt use the shorting pins, the worst that would happen is the load device would see no current.

Re: CTs & shorting pins #129944
11/23/05 02:13 PM
11/23/05 02:13 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Quote
When in doubt use the shorting pins, the worst that would happen is the load device would see no current.

Be careful here. If the load device is a protective relay, the relay will never cause the OCPD to open to clear a fault.
Don


Don(resqcapt19)
Re: CTs & shorting pins #129945
11/23/05 03:08 PM
11/23/05 03:08 PM
B
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
[Linked Image]

Here is a typical illustration of a shorting-block pole. [http://www.marathonsp.com/MSP%20CATALOG/2005%20Catalog%20pdfs/1500%20Series.pdf]

For multi-ratio (tapped) CTs, only two pins need shorting to prevent high open-circuit voltages across an open secondary. Be careful, though, not to lift the ground connections {typically X1} to prevent high electrostatically induced voltage from secondary to ground with energized equipment..

Also, besides no overcurrent-relay operation from left-in-place shorting pins, any sort of comparison-, unbalance- or differential-relay scheme can falsetrip during 'normal' operation.


[This message has been edited by Bjarney (edited 11-23-2005).]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
248,156 Are you busy
185,626 Re: Forum
174,985 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.004s) Memory: 0.9687 MB (Peak: 1.1099 MB) Zlib enabled. Server Time: 2018-07-22 03:00:40 UTC