ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 233 guests, and 10 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#129897 11/09/05 12:32 PM
Joined: Oct 2004
Posts: 132
M
Member
I have an instructor telling me that to do a VD calc, you use the following formula:
VD=(Amps x 1 way Length x R)/1000'

Where R = ohm/kFt from NEC Ch 9, Table 8

It seems to me like you would have to double the length since we are only counting the resistance in one direction...is this correct? I have always used the online calculators, and I'm trying to learn how to do it on paper.

Thanks, Mike

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Sep 2003
Posts: 650
W
Member
Yup. One way or the other you need to incorporate the round trip distance.

Some equations do this by fudging the resistance values (essentially using the resistance of 2000 feet of conductor, and reporting it as the resistance for 1000 feet 'there and back again')

Others look at the voltage drop on one side only because there is assumed to be no voltage drop in the neutral.

But in all cases there needs to be some consideration of the full circuit.

-Jon

Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
VD=(Amps x 1 way Length x R)/1000'
This would be the correct formula if you are
using a 240 volt 2 wire circuit. There is no return distance required.
If you have a 2 wire 120 volt circuit then you need to count the return distance in the caculation.

Joined: Mar 2005
Posts: 38
D
Member
Also, you need to use a return distance of the square of three (1.73) for a three phase circuit.


Dolphins Software

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5