Power Factor #129776
08/18/05 06:05 PM
08/18/05 06:05 PM
D
Dnkldorf  Offline OP
Member
Joined: Dec 2004
Posts: 1,064
nowhere usa
How does a Delta vs Wye change PF?

Any clues?


Dnk.....

Tools for Electricians:
Re: Power Factor #129777
08/18/05 10:53 PM
08/18/05 10:53 PM
B
Bob  Offline
Member
Joined: Feb 2002
Posts: 182
Mobile, AL, USA
How does a Delta vs Wye change PF?
It doesn't. Load has a specific PF. Voltage has nothing to do with it. A motor generally has a lagging PF and a capacitor has a leading PF. Check Here for more info. http://www.ibiblio.org/obp/electricCircuits/AC/AC_11.html


[This message has been edited by Bob (edited 08-18-2005).]

Re: Power Factor #129778
08/19/05 06:53 AM
08/19/05 06:53 AM
D
Dnkldorf  Offline OP
Member
Joined: Dec 2004
Posts: 1,064
nowhere usa
That's what I thought too.

I am doing PF testing and harmonics testing with a Fluke 434, and downloaded the new firmware to correct some bugs in it.

On a 480X240/120ct transformer I am monitoring, if you switch from delta to wye on the Fluke, the PF changes from .67 to .94.

I am curious why, they should be the same measurements unless somehow they get measured differently in the meter.

But that makes no sense..

Thanks.

Dnk.....

Re: Power Factor #129779
08/19/05 07:18 AM
08/19/05 07:18 AM
D
Dnkldorf  Offline OP
Member
Joined: Dec 2004
Posts: 1,064
nowhere usa
Or is it a Phase-Line PF, and then a Phase-Phase PF?

That would make sense, wouldn't it?


Dnk..

Re: Power Factor #129780
08/19/05 07:34 AM
08/19/05 07:34 AM
W
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
Only if the 'delta' connection tells the meter that the current sensors are in the phase to phase circuits, but the voltage connections are being made at the terminals.

Once you have the three conductors coming off the transformer, the power factor measurement should be the same.

-Jon

Re: Power Factor #129781
08/19/05 02:03 PM
08/19/05 02:03 PM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
A delta to wye transformer doesn't change the PF, but depending on how the meter makes the PF measurement, you may need to know that the delta to wye windings result in a 30 degree phase shift from primary to secondary.
Since PF is essentially measuring phase shift of voltage relative to current, that setting you describe on the meter may effect the reading.


Ron
Re: Power Factor #129782
08/19/05 03:41 PM
08/19/05 03:41 PM
D
Dnkldorf  Offline OP
Member
Joined: Dec 2004
Posts: 1,064
nowhere usa
It must be the phase-line reading, I measured another trans today and switched from delta-wye and the PF readings were about the same.

I will contact Fluke and let you know if your still interested.

Thanks for your help.

Dnk.....


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
mxslick
mxslick
Atomic City, ID USA
Posts: 803
Joined: October 2004
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
248,640 Are you busy
186,375 Re: Forum
175,860 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 14 (0.004s) Memory: 0.9834 MB (Peak: 1.1366 MB) Zlib enabled. Server Time: 2018-08-20 09:04:33 UTC